Re: Reliable Inverter Big Voltage Shuts Off Everything Under Medium Load
Too many possibilities for one device being the culprit for tipping the ballance when running the resistive heating load, the fridge, along with the freezers, not to mention the pool pump, are all in…1 · -
Re: Reliable Inverter Big Voltage Shuts Off Everything Under Medium Load
The symptoms in the video are consistent with an overload, if the inverter can support the heating loads most of the time but intermittently drops I would suspect there is a cyclical load such as a p…1 · -
Re: Reliable Inverter Big Voltage Shuts Off Everything Under Medium Load
The 30A rating for 10 AWG is taking into consideration length of run in typical installations, the actual current it is capable of carrying is significantly higher over short runs. Since the BMS pigt…2 · -
Re: Reliable Inverter Big Voltage Shuts Off Everything Under Medium Load
The inverter is likely not the cause but rather voltage drop due to under capacity batteries, under sized or too long DC conductors, poor treminal connection, failing batteries, or a combination of a…2 · -
Re: Lithium expert help needed...
Looks to be an experimental setup, the battery capacity is probably just sufficient to satisfy the idle demand. There is nothing wrong with how the batteries are configured, there are pros and cons t…1 ·