Re: It's going to be close to cost effective! or Off grid at 26 cents a KWh!
Re: It's going to be close to cost effective! or Off grid at 26 cents a KWh! My first reaction is that regardless of how carefully you treat your batteries, and how good a set of batteries you get, a…1 · -
Re: Choosing a good generator
Re: Choosing a good generator The major difference is that a burner designed to just produce heat will be run with a high enough air to fuel ratio to provide for complete combustion. There will be es…1 · -
Re: PWM versus MPPT- a quick analysis
Re: PWM versus MPPT- a quick analysis One exception to that which can extend the stage(s) over which MPPT gives an advantage: If you have daytime opportunity loads which you can schedule to happen wh…1 · -
Re: Load vs Line side of Circuit Breaker
That is correct if you have installed the CB for protection only. If you are also going to use it as a switch to disconnect the panels while they are producing current, then the breaker may not survi…1 · -
Re: Moisture in Inverter
The condensation of moisture on the window is a sign of two things: 1. The air in the basement is cooler than the air inside the working inverter. (Not at all surprising). 2. There is liquid water so…1 ·