  • Wind charge controller question

    Is there such a controller that when the batterys are full it disconnets the wind generator from the batterys and then brakes the generator. Brakes meaining it switches the wind gen to resistive load and eventualy shorts the generator leads. All the charge controllers I've found have the wind generator hooked directly to the Battery and a diversion load running from the battery's when fully charged. I don't want a diversion load running constantly from the batterys and want the wind gen to stop or be significantly slowed when no longer needed. So the wind gen is only connected to the batterys when needed.
    Last edited by machineman; November 14th, 2011, 20:10.
    Off-Grid: E-Panel Magnum MSAE4024 Inverter/Charger, Xantrex CC XW60, 24V 440ah (costco batterys), Evergreen ES Panels (1600w)

  • #2

    Re: Wind charge controller question

    Re: Wind charge controller question

    In theory, you just need the diversion charge controller set to turn on a single pole (break before make), double throw relay to disconnect the wind turbine +lead from the battery and connect it to the -lead (return) to the wind turbine. The "dead short" should provide enough torque to stall the blades. (Common to ++ead; N.O. to +Battery; N.C. to -Lead/battery ground of wind turbine--Or switch NO and NC to reduce relay power draw).

    In practice, I have read (here?) of at least one wind turbine that overheated the windings in the alternator when in "shut down" (shorted output).

    You could setup a little programmable controller that did a two stage switching, first to a resistive load (slow down without high current surge), then a few seconds later shorted out the heater to make the full current/stall condition.

    I agree that it would seem to be a better idea (less turbine "on time", so less bearing wear, etc.).

    However, I have not seen anybody talk about building/testing such a controller here.

    Also, you probably want some sort of backup/fail safe setup... I believe the NEC actually requires a second, independent, dump controller and load because of the results of failure (overcharged battery bank may cause fire, and for me, a run-a-way turbine starts shedding parts).

    For commercial turbines, they probably have two or three ways of shutting down for redundancy (brake, shunting, feathering blades, turning sideways to wind are a few I can think of--Can you do that with your controller and some sort of actuators?).

    -Bill
    20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

    Comment


    • #3

      Re: Wind charge controller question

      Re: Wind charge controller question

      Originally posted by BB. View Post
      In theory, you just need the diversion charge controller set to turn on a single pole (break before make), double throw relay to disconnect the wind turbine +lead from the battery and connect it to the -lead (return) to the wind turbine. The "dead short" should provide enough torque to stall the blades.

      -Bill
      That's the set-up that I had when I had the "Hornet". Worked great in low to medium wind speeds. But I got a total shock when during one of our famous Fall Tropical Storms that come up the Atlantic Coast, we had some pretty brisk winds. Finally when the blades were threatening to launch an attack against our American Neighbors a thousand miles away, and knowing such an attack might well be answered in a rather unpleasant way, I applied the short circuit to shut it down. Much to my surprise and horror, there was so much power in the wind that it made absolutely no difference whatever. The sparks flew from the contacts on make and break, but the turbine showed no response whatever.
      And no, I no longer have the Hornet.
      1900 watts PV, (1000 watts PV feeding MidNite Classic 150; 900 watts PV + 160 watts micro hydro both feeding into a single shared Morningstar TS-MPPT-60) ; Xantrex Pure Sine 1800/12 for heavy loads; Xantrex Pure Sine 1000/12 on 24/7 for everything else; six Rolls Surrette 2 volt L16 @ 12 volts.
      Domestic hot water totally provided by the sun 8 months out of every year via thermal panel.

      Comment


      • #4

        Re: Wind charge controller question

        Re: Wind charge controller question

        Don't let that happen again Wayne "...now go away or I shall taunt you a second time."

        -Bill "Monty Python" B.
        20x BP 4175B panels (replacement) + Xantrex GT 3.3 inverter for 3kW Grid Tied system + Honda eu2000i Inverter/Generator for emergency backup.

        Comment


        • #5

          Re: Wind charge controller question

          Re: Wind charge controller question

          Originally posted by BB. View Post
          Don't let that happen again Wayne "...now go away or I shall taunt you a second time."

          -Bill "Monty Python" B.
          Hahahahahaha - - - - :
          1900 watts PV, (1000 watts PV feeding MidNite Classic 150; 900 watts PV + 160 watts micro hydro both feeding into a single shared Morningstar TS-MPPT-60) ; Xantrex Pure Sine 1800/12 for heavy loads; Xantrex Pure Sine 1000/12 on 24/7 for everything else; six Rolls Surrette 2 volt L16 @ 12 volts.
          Domestic hot water totally provided by the sun 8 months out of every year via thermal panel.

          Comment


          • #6

            Re: Wind charge controller question

            Re: Wind charge controller question

            One Idea I have is to use the Aux ouput on my solar Xantrex XW CC to trigger a wind gen disconnect and brake at a pre determined voltage, maybe 28V or so. The Aux could easily drive an SSR. The sticking point is building a circuit that runs in timed sequence which is safe to the hardware.

            1. Disconnect from Batterys.
            2. Slow down turbine.
            3. Stop turbine.

            The main reasons for not using a constant diversion load and wanting to brake the wind turbine are:
            -- All my Solar batterys, CC, Inv, etc are in a small close concrete shed. Running a heating diversion could over heat this area. I only visit once a month and that worries me.
            -- Wind Gen lifetime and wear.
            -- Don't wnat to interupt the float cycle of my solar system with a diversion load kicking in.
            Off-Grid: E-Panel Magnum MSAE4024 Inverter/Charger, Xantrex CC XW60, 24V 440ah (costco batterys), Evergreen ES Panels (1600w)

            Comment


            • #7

              Re: Wind charge controller question

              Re: Wind charge controller question

              Originally posted by machineman View Post
              One Idea I have is to use the Aux ouput on my solar Xantrex XW CC to trigger a wind gen disconnect and brake at a pre determined voltage, maybe 28V or so. The Aux could easily drive an SSR. The sticking point is building a circuit that runs in timed sequence which is safe to the hardware.

              1. Disconnect from Batterys.
              2. Slow down turbine.
              3. Stop turbine.

              The main reasons for not using a constant diversion load and wanting to brake the wind turbine are:
              -- All my Solar batterys, CC, Inv, etc are in a small close concrete shed. Running a heating diversion could over heat this area. I only visit once a month and that worries me.
              -- Wind Gen lifetime and wear.
              -- Don't wnat to interupt the float cycle of my solar system with a diversion load kicking in.
              The disconnect voltage although set to 28v must allow for some hysteresis. Basically, a high gust of wind can temporarily raise the voltage to 28v and then the voltage will fall back once the gust is over. You'll need a circuit to disconnect only if the 28v is held for some time, a minute say.... I have built something similiar but instead of braking, I'm switching between 12v and 24v battery sets. My braking system is manual.

              I've blogger here what I just described above. I'm no electronics expert however you can get some ideas from my circuits and adapt them to your needs.

              Regards
              Brian
              9 IBC Solar 235W Panels, SMA SB2100TL grid tie inverter for a 2KW grid-tie system, Backup system: 1080W PV @ 24v, Modified Air-X 12v/24v Marine, 500AmpHr Battery Bank, Infinitum Desulfator, 600VA UPS, home built 200l solar water heater, 20K BTU Solar Assisted Air Conditioner - TeecoGroup.
              Personal Website

              Comment


              • #8

                Re: Wind charge controller question

                Re: Wind charge controller question

                My good old Southwest windpower H80 controller does what you ask. \You can set the controller's setpoints to whatever voltage you want diversion to start/stop at, and there is a resistive load (looks like toaster wires) integrated in the controller. When the "on" setpoint is reached power diverts to the heat dump, when the "off" setpoint is reached on the way down the "toaster" shuts off and the controller reverts to charging. And like Wayne, my short-out brake works in light to medium winds only.

                I used to brake it when heavy winds were expected until my wife woke me at 2 am and asked if we should be hearing the stall flutter...the wind had overcome "braking" and started the turbine up to maximum speed. We don't bother to brake anymore.

                Ralph
                http://enlighten.enphaseenergy.com/p...stems/hY7W5536
                see the project buildhttp://www.greenpowertalk.org/showthread.php?t=11702

                Comment


                • #9

                  Re: Wind charge controller question

                  Re: Wind charge controller question

                  I've got one of these but don't know if it would work on yours. http://www.tlgwindpower.com/ccontrollers.htm
                  5 Evergreen ESA 210's mounted, 4 Evergreen ESA 215's in the closet, Outback FM80, Xantrex Prosine 2, 4 Sunextender 8D batteries. 1 TLG wind generator. WB8ZMY Kirk