Breaker??
54d18
54d18 Solar Expert Posts: 81 ✭✭✭
I have a 1750 Eliminator Inverter, made by Xantrex
for Canadian Tire.
My question is about installing a breaker to the
DC side of the inverter, I have a 600V 3 Phase breaker,
could I use this since I already have it?
    Re: Breaker??
    no. you need a breaker rated and approved for dc operation. you might even consider a fuse as that is sometimes a cheap alternative to a cb.
  • 54d18
    Re: Breaker??
    What if all 3 legs of the breaker are wired
    in series to break the load, as is done
    with relays to lengthen contact life?
    Re: Breaker??
    Nope.
    DC current is able to 'jump' further than AC. In order to safely interrupt the circuit, DC rated equipment has to 'break a larger gap' to prevent arcing. This can't be done by breaking it in three places, which is what would happen wiring the 3-phase the way you suggest.
    Fuses aren't that expensive: http://store.solar-electric.com/infubr.html
  • RCinFLA
    RCinFLA Solar Expert Posts: 1,484 ✭✭✭✭
    Re: Breaker??
    Technically most high voltage, high amperage AC breakers will work fine.
    The problem is they have not been DC approved by UL so regulatory wise they can not be used.
    There just isn't enough demand for DC breakers for the companies to pay the extra expense and time to get the additional DC rating UL approval. The exception is Square-D has a line that has both AC and DC use UL approval. Believe the designation is QOU breakers.