voltage drop 12- 15 ft inverter cables
John XW NY
Solar Expert Posts: 50 ✭✭✭✭
What would the voltage drop be from 12- 15 ft 4/0 cable from inverter to battery bank?
what would be the proper method of dealing with this issue?
is 4/0 good enough to negate that?
Re: voltage drop 12- 15 ft inverter cablesJohn XW NY wrote: »What would the voltage drop be from 12- 15 ft 4/0 cable from inverter to battery bank?
Depends on the Amps drawn, more amps = more dropPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Assuming a XW 4024 used at full capacity (8kW surge?), 85% inverter efficiency, and 21 volt minimum:
Amps = 8,000 watts * 1/21 volts min * 1/0.85 eff = 448 amps maximum
You have 15' run of cable, and for this calculator (voltage drop calculator) , use 2x15'=40' of wire, 100F--you get:
Drop= 0.70 volts
%Drop= 2.94% (based on 24 volts)
For 4kW max operating current, 0.35 volts and 1.47% drop.
In general, keeping those heavy current leads between charge controllers and inverter to the batteries as short as practicable is a good idea.