I’m looking at using a rotary marine battery disconnect switch for my off grid battery bank.

http://bluesea.com/category/1/productline/3

Its rated 350A cont. 1750A inrush.

My 12VDC input inverter is 2kW Cont. 4.5kW Surge. Bank of 4 GC2 220ah Batteries, 4/0 Cabling, 300A fuse.

Does anyone have experience with using this type of switch for off grid installations?

Thank you,

Jerry

Comments

  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Re: Marine battery disconnect

    although i don't have one, i haven't heard of any complaints and it should work just fine.
  • System2
    System2 Posts: 6,290 admin
    Re: Marine battery disconnect

    it is a newbie question.

    when or where battary disconnect is need for off grid installation.

    TheWire wrote: »
    I’m looking at using a rotary marine battery disconnect switch for my off grid battery bank.

    http://bluesea.com/category/1/productline/3

    Its rated 350A cont. 1750A inrush.

    My 12VDC input inverter is 2kW Cont. 4.5kW Surge. Bank of 4 GC2 220ah Batteries, 4/0 Cabling, 300A fuse.

    Does anyone have experience with using this type of switch for off grid installations?

    Thank you,

    Jerry
  • crewzer
    crewzer Registered Users, Solar Expert Posts: 1,832 ✭✭✭✭
    Re: Marine battery disconnect

    If nothing else, a a battery disconnect switch comes in handy when assembling or maintaining a system.

    I used the 350 A model for several years with no problems. A heavy duty model is also available: http://bluesea.com/category/1/productline/4

    Even better would be a big DC rated breaker with a high AIR rating (20 kA to 50 kA).

    HTH,
    Jim / crewzer
  • SolarJohn
    SolarJohn Solar Expert Posts: 202 ✭✭
    Re: Marine battery disconnect

    I use one to switch between my old and my new battery banks. Having the ability to switch in 1, 2, or both is really handy.