I recently installed a 30 amp The Kid mppt charge controller,a breaker box, and a 600 watt inverter into a small box, it sits at eye level, the box is painted a dark brown, it has been getting to hot in there, I installed a couple 2 " louvers, I do plan on painting the box white, I keep the door ajar to keep it cool. I was thinking about installing a fan, would it be best to put in a temperature sensor as well or a timer? If someone has had this problem I would be curious how they solved it,besides leaving the door ajar.

Comments

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    The first thing that occurs to me is a large-ish heat sink. Basically a piece of metal with a large surface area moving heat from a source to a sink.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    The Kid comes with installation instructions and requirements for ventilation. It dissipates heat and must be cooled

    Inverters are the same, they produce even more heat and need airflow.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||