Schneider Electric (Square D) AC Disconnect Recall
BB.
Super Moderators, Administrators Posts: 33,447 admin
Just an FYI,
I received this notice from my utility (PG&E) about a Square D Brand General Duty Safety Switch 30/60A, 120/240Vac, NEMA 3R recall.
Some date code/models do not open the internal knife switches when the outside handle is thrown. Apparently (reading the recall notice), if the switch does function correctly (switches open when outside handle is moved to OFF), then all is OK.
https://www.schneider-electric.us/en/download/document/3130HO1801/
https://download.schneider-electric.com/files?p_enDocType=Handout&p_File_Name=Exhibit+C.pdf&p_Doc_Ref=3130HO1801 (link to file, if does not work, use above link)
REFERENCE: PRB-207512 Square D Brand General Duty Safety Switch 30/60A, 120/240Vac, NEMA 3R
Inspection procedure regarding the following catalog numbers manufactured within date codes 1401 – 1803 (January 1,
2014 – January 18, 2018). The safety switch can potentially remain energized when the handle is in the "OFF" position.
This poses a potential risk of an Electric shock or Electrocution hazard to customers. Refer to Table 1: Impacted
Catalog Numbers for impacted references.
Table1: Impacted Catalog Numbers
DU222RB DU322RBUP D221NRBUP DU221RBUP DU222RBUP D211NRB D321NRB CD321NRB DU321RB D211NRBCP D321NRBCP DU321RBCP DU321RBUP D221NRB D321NRBUP DU322RBCP DU322RB D221NRBCP DU221RB
-Bill Table1: Impacted Catalog Numbers
I saw a service note on this about 2 months ago Bill. I was glad it was not the 600vdc model
This recall unit would probably be required with a grid/batteryless inverter."we go where power lines don't" Sierra Nevada mountain area
Yes, this model was used for my GT System ac disconnect. However, my system is way older than these date codes.
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
- 626 Discussion Forums/Café