combiner breakers
The comb like thing, just inserts were the wire would and you tighten down on it...
The spacing is different on either side for fuses or breakers.
The only 'trick' to making your own is adding a lug for the combined output.
but you dont have to use a copper plate bussbar,correct?? You can just wire it all up..??
The buss really just makes it easier to make a good, solid, secure parallel connection. Getting a good connection with more than 2-3 large-ish wires can be harder with just the wire, but it can be done.Off-grid.
"Bus Bars" are a large class of objects... For example, here are some common ones used in wiring:
https://www.solar-electric.com/marine-rv/installation-supplies/terminal-bus-bars-ground-bars.html
Some people have taken copper water pipe, smash flat, drill holes, and made bus bars out of them.
Member @2manytoyz has a nice website. About 1/2 way down, he has a set of links/pictures that show the evolution of his backup solar power system. Lots of Do It Yourself information:
http://2manytoyz.com/
ws ..,
Each of those MidNite MNEPV breakers has two screws -- one at the top, and the other toward the bottom of the breaker. The busbar fingers slip into the terminal of the breaker at the top, and the screw on the terminal secures the breakers mechanically, and also makes the common connection for the output of the Combiner, to the CC PV input.
That Tin-plated busbar is included with the MNPV6 Combiner. Often the MN Combiners have segmented output busbars, which allow feeding separate PV array to each of two CCs. For a single CC, the segment busses are sandwiched together, and connected and held by the output terminal for the PV cable.
The busbar stabilizes the row of the breakers. Without making your own busbar (if you are making your own Combiner), then you will need to place two wires into the top of most of the breaker terminals (not advised) , or make your own busbar.
Is this something that you really want to do ?
You can buy the correct busbars at the WInd-Sun store, and they are not that expensive, of course, neither is the whole Combiner (IMO).
FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.