VancleVector: well pump popping breaker

Options
This discussion was created from comments split from: Automatic Transfer Switch issues (?).

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    Either the genset (?) Cannot power the pump, or the pump takes a lot of current to start (bad starting capacitor  low genset voltage, etc.).

    Try wiring to the genset directly. Long wire runs with too much voltage drop?

    Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    With the generator un-wired, probe the connection points and verify you actually have 240V there and not 120V
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited July 2018 #4
    Options
    What other loads are applied to the generator?  A battery charger for example could be drawing a significant amount of current, but without details, one can only speculate.