Hi,

Can charge controllers be undersized regarding wattage, similar to the way inverters can be undersized? By undersized, I of course mean compared to the rated PV capacity.

Comments

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Depending on location and controller, reasonable overpanelling (~20%) is okay IMHO. Most decent controllers should protect themselves, and having extra pv makes for better charging on hazy / light overcast days.

    That said, running controllers constantly at rated capacity will make them run hotter than otherwise, and may shorten their lifetime.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited May 2018 #3
    Q. Can a pickup truck rated to carry a load of 3/4 ton actually carry a load of 1 ton?
    A. Probably but the added stresses imposed will dramatically shorten the expected life expectancy  of the components over the long term
    An analogy, yes, but relevant.

    Q. Can a 3 ton truck carry a load of 1 ton
    A. Yes, every day, without fatigue of its components.

    It's the same with electronic components, lower stress leads to longer life.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Carrying on with the truck load analogy, we have to consider that gravity(ie insolation and actual pv potential) is not a constant.  In a hazy coastal environment, the "1 ton load" might only rarely actually weigh more than the 3/4 ton rating.  In a clear alpine environment, it might actually be more than a ton.  There's also the size and type of battery to consider.  Sort of like considering whether the load is going over bumpy, hilly roads with lots of sharp curves and a live load rolling around in the bed, or flat blacktop with a stable load.

      
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • schmek
    schmek Registered Users Posts: 34 ✭✭
    Noted, thanks guys. I find lots of information about how inverters are undersized, but nothing of charge controllers being undersized. 
  • BB.
    BB. Super Moderators, Administrators Posts: 33,431 admin
    edited May 2018 #6
    Note that there are two major types of solar charge controllers:

    PWM: Pulse Width Modulation--More or less a transistor that turns ON/OFF between solar array and battery bank. This type of controller, you cannot over panel without causing them to shutdown/overheat/damage.

    MPPT: Maximum Power Point Tracking--These are use a "DC to DC" Converter internally (tech talk--typically a "buck mode" DC to DC converter). These controllers can safely and reliably "throttle their maximum output current to "rated value" without damage. We typically suggest a maximum over paneling of ~ 1/0.77 (1.3x MPPT's rated power) for a cost effective installation. Hot solar panels tend to have less than rated output Wattage (actually Vmp falls as solar cells/panels get hot---Pmp=Vmp*Imp).

    But, as always, heat (and thermal cycling) is the enemy of all things electronic (virtually anything "ages" faster when hot). If you run a controller at 100% of rated power all day long--It probably will not run for as many years as a controller that runs at 50% rated output.

    The technical side--For every 10C (18F) increase in temperature, the "thing" will last 1/2 as long (70F = 100% life, 106F = 1/2*1/2=1/4 as long as life). Also, thermal cycling is a huge factor in failures (simply going from cold to hot back to cold every day).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • fratermus
    fratermus Registered Users Posts: 48 ✭✭
    > I find lots of information about how inverters are undersized, but nothing of charge controllers being undersized

    Try googling "overpaneling" instead of "undersized";  should be more info.