Pete4049Pete4049 Posts: 4Registered Users
Should I install a switch in the cable leading from my battery bank to the inverter.  What is the switch protecting?  The cable or the inverter or both?  Should there be a switch in the cable between the charge controller & the battery bank?  Do I need both switches?  Thanks, Pete
Tagged:

Comments

  • 706jim706jim Posts: 213Solar Expert ✭✭✭
    Or a high capacity circuit breaker. There's nothing quite like the surprise of a high amperage short circuit and you have no way of disconnecting it.

    Think "Fire".
    Island cottage solar system with 1400 watts of panels, Trace DR1524 MSW inverter, Trace C40 PWM controller 8 Trojan L16's. My 25th year.
  • mcgivormcgivor Posts: 2,164Solar Expert ✭✭✭✭✭
    edited May 4 #3
    Installing DC rated circuit breakers in both positions, sized appropriately to protect the conductors feeding the inverter /battery, will not only provide a convenient service disconnect but also protect the conductors in the event of a short circuit. Batteries can supply enormous amounts of current which should never be underestimated, a fused disconnect, or fuse plus disconnect could bu used but must be DC rated for the appropriate voltage / current, but cost wise breakers tend to be the more economical in the long run as a blown fuse needs replacing, whereas a breaker would require resetting. The purpose of overcurrent protection is to protect the conductors not the device fed by the conductors.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery bank 