Yes, another beginner with obvious questions... confusing battery and trying to figure out setup

TempogenTempogen Posts: 1Registered Users
Hello all, 

I've been struggling with this for months and i'm hoping I can finally solve it with your help. 
Basically I have about 30 Shoto GFM-2000 batteries, and I also have a power problem, and I do think I can put them to good use. 
I've been trying to use this site : 
http://www.freesunpower.com/battery_designer.php

To kind of find the right setup to use some of these batteries as backup power for a large fridge I have. 
I know that the voltage of the battery is 2v, and the amperage is 2000, but other than that i'm stumped and can't figure anything out. 
i'm sure you guessed by now that i know nothing about power or electrical engineering. Unfortunately in my location I couldn't get any professional to check it out for me either. 

So I turn to you for advice on what little info I gave. How to at least translate the specs of this battery : 
http://www.rectifier.co.za/Batteries/Shoto/psdf/GFM-2000.pdf

To use with the above site, or if you have any advice at all to use these with an inverter to be charged using my 220 v AC so that they'd be the backup power during power cuts. 

Thanks 

T

Comments

  • littleharbor2littleharbor2 Posts: 914Solar Expert ✭✭✭✭
    Provided these batteries are not worn out, you can series wire 24 of these into a very good size 48 volt bank. The other 6 could be wired up for a 12 volt bank and worked or kept on float till you find out if all 24 other batteries are healthy. If you decide to go the solar route be prepared to spend a good amount of money for the panels and charging components and inverter necessary to charge this large capacity battery. 

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 700 ah @24 volt AGM battery bank. Plenty of Baja Sea of Cortez sunshine.

  • EstragonEstragon Posts: 2,310Registered Users ✭✭✭✭
    The wiring of the batteries will be determined by the DC input voltage of the inverter (typically 12, 24, or 48v). Inverters large enough to start and run compressor motors in fridges tend to be 24v or larger.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mcgivormcgivor Posts: 1,747Registered Users ✭✭✭✭
    The batteries appear to be designed for standby use, according to the attached pdf.which would be useful in a backup situation. Being that 220 Vac is the nominal, I would highly recommended using a 48V battery arrangement or 24 in series with an appropriate inverter, this would keep conductor/circuit breakers and so forth sizes to a minimum. What is the charging source, an important piece of the puzzle.?
      1500W, 6× Schutten 250W Poly panels , Schneider 150 60 CC, Schneider SW 2524 inverter, 8×T105 GC 24V nominal 

  • littleharbor2littleharbor2 Posts: 914Solar Expert ✭✭✭✭
    They do have voltage specs for cyclic use in the spec sheet.

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 700 ah @24 volt AGM battery bank. Plenty of Baja Sea of Cortez sunshine.

  • PhotowhitPhotowhit Posts: 4,529Solar Expert ✭✭✭✭
    It sounds like batteries for the correct use, stand by UPS. Setup in a 24 volt configuration, I would recommend using tinned copper bar inter connects. Figure out the maximum load you will have and purchase an inverter charger for the load. you may find that due to the expenses of such a large inverter-charger you choose to only power a limited amount of your usual loads. Purchase and install the inverter-charger and wire accordingly. If it will cover all your loads you could choose to have all the incoming current pass through it. If not you  would want to either install it for a single circuit. Or have it installed with a transfer switch so you can manually shut down loads before you turn it on.

    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Prosine 1800 and Exeltech 1100, ForkLift battery. Off grid for @13 of last 14 years. 1000 watts being added to current CC, @2700 watts to be added with an additional CC.
  • Ski66Ski66 Posts: 11Registered Users ✭✭
    Something to consider is the BOS, as that is quite a large battery bank. I agree more information on the charging source would be helpful to decide to go with a 24 or 48 volt system, as the cost on the CC, and inverter will vary depending on what battery bank you decide to go with, also consider the line run to your charging source, and the line loss will also vary by what voltage you go with, However I found that www.sunextender.com has great diagrams for all battery banks, you may want to check it out, at the bottom of thier site you can download and view all the options for your battery bank. Hope this info is helpful.