Balancing the Loads of my Conext SW with an Autotransformer

MrM1MrM1 Posts: 72Registered Users ✭✭
The Schneider SW Inverter series has a feature that is suppose to allow the user to draw from batteries until a user set threshold has been reached.  That threshold can be set to Battery voltage, which would allow the loads to be supplied by battery,  until a low battery threshold was reached,  and then the inverter would  switch over to grid power.   This can be set by a low voltage threshold, or if one has the battery monitor,  can alternately be set up on the SOC of the battery.  Schneider calls this AC Support mode.   And their load shaving "works" in a similar fashion.

Bad news,  it does not work very well.  The documentation states ...

"AC Support ensures that no current comes from the AC Input connection of the Conext SW as long as the battery’s state-of-charge (SOC) or battery voltage conditions allow it."  p 1-7

This really is not the case at all.  And Schneider has told me that this line should not even be in the documentation. 

That being said,  Apparently ... also according to Schneider, for the SW series inverters to have any success at even partial grid interactivity,  The loads must  be balanced on L1 and L2 (the SW series is a split phase 240v inverter).    The better balanced the loads,   the better the grid interactivity works so it seems (or has at least been my experience)

But as an example,  right now:
- my SOC is 88% and my battery bank voltage is 25.6v (24v system)
- I have the AC support mode set to 23v which means the system is suppose to run off batteries UNTIL my batteries reach 23v.
- Yet right now,  my loads are 1355w,   and I am pulling 18w from the batteries,  and 1337w from the grid.  
- AC Support mode is on, but obviously not working very well.  So much for the grid support for the batteries
- BUT ... my Loads are imbalanced.  I cannot change this as right now L1 is powering a 120v water heater,  and L2 is powering some LED lights and a fridge that is presently in the saving mode of its cycle.
- L1 is drawing 10.7 amps AC,  L2 is drawing .8 amps AC

While I have never seen AC support mode work as described above,  I have seen it work at about 20% grid / 80% battery when 2 conditions are met:
1. loads are fairly balanced
2. AC output is fairly hi .... upwards of 2000 watts for my 3400 watt inverter.

The higher the wattage goes up, the more the system will draw off batteries as long as there is fairly good load balance and one is inside the set threshold.    But balance is difficult to achieve all the time.  And hi watts are very impractical for all but the largest of battery banks.

So I am wondering and  thinking about Auto transformers to help overcome this.    Would something like the Outback FW-X240, which is made for 2 120v stacked Outback transformers,  work with my SW which is in a single  box,  but has 2 120v lines?

If I could use some thing like the FW-x240, or some other auto transformer possibly locally sourced,  could I not balance my loads and have much better success with Schneider's ill working AC Support mode?

How possible would this be? 

Would I need to contact Schneider for the proper size and spec of an Auto Transformer,  or would something like the OUtBack FW-x240 work out of the box,  or could I go with those specs to an AC supply house to get one like it?   Just wondering as this would sure get my SW working a whole lot closer to my original design for the whole solar system.  It was a major disappointment to learn from Schneider that their AC support mode really does not work as advertised.    And a major culprit seems to be unbalanced loads.

Any thoughts or help?  Ideas? 

Attached is a diagram from Outbacks info on how this could possibly work.  Could something like this work?   What am I missing?  Is there a less expensive way to do this and balance loads?    I realize with the Outback I am looking at 2 inverters, but they are 120v each and mine is a 240 split. 



REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
Grid-Assist Off-Grid / Need 3200Whs Daily
System, Pics and Discussion

Comments

  • mike95490mike95490 Posts: 7,558Solar Expert ✭✭✭✭
    Yes, and autotransformer is used to balance loads.

    No, I don't know the exact connection to accomplish this.   BUT, I suspect, any transformer with a CT 240V winding, of sufficient gauge/VA to handle at least 3/4 of your inverters power, would do it.   But why not wire that heater to 240V and spare a LOT of trouble? That heater is a huge imbalance and I'm surprised the inverter even tolerates it
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • MrM1MrM1 Posts: 72Registered Users ✭✭
    mike95490 said:
    Yes, and autotransformer is used to balance loads.

    No, I don't know the exact connection to accomplish this.   BUT, I suspect, any transformer with a CT 240V winding, of sufficient gauge/VA to handle at least 3/4 of your inverters power, would do it.   But why not wire that heater to 240V and spare a LOT of trouble? That heater is a huge imbalance and I'm surprised the inverter even tolerates it
    Because I cannot find a full size element in 240v 1000-1300 watts.   I am using a 240v 4500W element at 120v which yields right at 1150 watts.  But I also want to better balance all my loads at all times for that very reason,  so my inverter will better tolerate and perform better in AC support mode. 

    I discovered last night that if I just run my well pump as the load,  which after start up runs at about 800 watts .... as  240v load it is perfectly balanced, and the inverters AC Support mode performs near perfectly.  It supplies the load from the battery except for the 2% supplied by the grid to prevent back feeding of the to the grid.
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • mike95490mike95490 Posts: 7,558Solar Expert ✭✭✭✭
    Here's how an auto transformer looks schematically   ( from https://www.electronics-tutorials.ws/transformer/auto-transformer.html )

    grainger has several 240V, 750 & 1,000 w elements, and then you could use a fairly smallish (lower losses) transformer,
    by shifting the big 120v loads, to 240V.  Maybe the microwave & blow dryer would need a larger transformer to support them but how many hours do they actually run, and is a $500 transformer worth $20 of electricity ?






    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • MrM1MrM1 Posts: 72Registered Users ✭✭
    edited March 17 #5
    mike95490 said:
    Yes, and autotransformer is used to balance loads.

    No, I don't know the exact connection to accomplish this.   BUT, I suspect, any transformer with a CT 240V winding, of sufficient gauge/VA to handle at least 3/4 of your inverters power, would do it.   But why not wire that heater to 240V and spare a LOT of trouble? That heater is a huge imbalance and I'm surprised the inverter even tolerates it
    I suppose I could use a step down transformer on the water heater element and run it 240v out of the inverter thru the step down to 120v.   Would something like that work?  Then at least I would be balancing that load.

    Would something like this work on the single water heater load so I could run it 240v out of the inverter but keep it at 120v at the water heater?

    https://www.cesco.com/Square-D-by-Schneider-Electric-50SV1A-Schneider-Electric-50SV1A-Square-D-050KVA-TFMR/p1891141

    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • MrM1MrM1 Posts: 72Registered Users ✭✭
    edited March 17 #6
    I've seen those elements.   they are very short.   Wouldn't that have an adverse effect on the way they heat water if they only extended into the tank 7-8" as opposed to the double loop tpye i have that go in 13"

    But if I use a 240v element,  than I would not have to worry with a transformer as it would run both sides of the inverter,  but the wiring size may have to increase because of current.  Though I doubt it at 700 - 1000 watts.
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • mike95490mike95490 Posts: 7,558Solar Expert ✭✭✭✭
    MrM1 said:    ......
    But if I use a 240v element,  than I would not have to worry with a transformer as it would run both sides of the inverter,  but the wiring size may have to increase because of current.  Though I doubt it at 700 - 1000 watts.
    240V loads generally, use less amps than the same load at 120V
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • mike95490mike95490 Posts: 7,558Solar Expert ✭✭✭✭
    MrM1 said:
    Would something like this work on the single water heater load so I could run it 240v out of the inverter but keep it at 120v at the water heater?
    That transformer is good for about 50watts and only about 5 lbs of iron.   Your 10A water heater @ 120V is 1200 watts, and that will need at least a 1.3KVA transformer around 30# or so.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • jonrjonr Posts: 930Solar Expert ✭✭✭✭
    >  Wouldn't that have an adverse effect on the way they heat water if they only extended into the tank 7-8"

    I don't think so - water that is free to convect moves lots of heat.
  • MrM1MrM1 Posts: 72Registered Users ✭✭
    Right now I am set to try the 1000 W 240v water heater element at 6.50.  Much cheaper than a auto transformer.  Also going to call Schneider tomorrow and see what they recommend,  but I suspect that the Outback will probably be the most economical. 

    Also, I had no idea it was that large.  I think 10" x 11".  That will be larger than my current switch gear box can handle and would have to me mounted in a separate box.  

    Thanks for the guidance. 
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • EstragonEstragon Posts: 2,047Registered Users ✭✭✭✭
    The x240 is also on the heavy side (sturdy shelf needed) and makes a slight buzzing noise, which may or may not make a difference in locating it.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • MrM1MrM1 Posts: 72Registered Users ✭✭
    Connecting a 240v 1000w water heater element by itself to my Conext SW inverter allowed the load to be perfectly balanced,  AND the AC support mode worked flawlessly.   So it is confirmed that Schneider's AC Support mode needs a very balanced load over L1 and L2.

    So I called Schneider Tech Support and asked if they recommended an Auto Transformer. They did not have one the specifically recommended.  

    And then they asked why I would want an Auto Transformer ... To run L1 and L2 step down to a single 120v?    I told them, No,  I would use it to balance the load coming off L1 and L2 from their SW inverter so that the AC Support mode would actually work.  And Tech Support was pretty amazed and said,  yes that would actually work very well.  And that they had never thought of that. 

    As poorly as the SW's AC support mode actually "works" ... I'm surprised it does not come preinstalled in the inverter ... or at least that the do not have a Technical Bulletin recommending it. 
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • MrM1MrM1 Posts: 72Registered Users ✭✭
    So what, besides costs, is the difference between the PSX-240 and the FW-x240.  I realized on is 6Kva and the other is 4Kva,  but is it just that the PSX comes in a housing, has a fan and a double pole breaker? 

    I really do not need the 6Kva of the PSX

    Would I need a fan on the FW-x240?    Could it just be mounted in a box large enough to handle it's size? 

    Also, would such a transformer be suitable to mount in a craw space 3 feet above ground under a house,  not exposed to the elements,  fully enclosed so not open to animals etc, but subject to outdoor temps?    My water heater is already under there.  Plenty of room for working.  Just not sure if a transformer can be mounted in such a location.   If no I would mount it in my garage,  which really has the exact same conditions,  only diff is the concrete floor.
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion
  • mike95490mike95490 Posts: 7,558Solar Expert ✭✭✭✭
    They both are the same transformer, one has fan cooling to gain the extra 2 KW.  It's not likely you would need the fan.
    The transformer needs some sort of protection (I've got a PSX) not sure what sort of cabinet the FW comes with, but you need to
    have strain relief so the transformer wires are not strained by the hook up cables.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • EstragonEstragon Posts: 2,047Registered Users ✭✭✭✭
    I have the version in a box. I've never heard a fan run, but it just powers a pump that runs for a few minutes at a time.

    I know critters get into my crawlspace , so I'd want it in some sort of chew-proof box, and it needs OCP, so I'm not sure getting the transformer alone is much of a savings. To each his own though.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • MrM1MrM1 Posts: 72Registered Users ✭✭
    edited March 21 #16
    Thanks.  I'd mount it in a steel / metal vented box.  Probably lag it to floor joists and install insulated buss bars for the connections.   
    REC TwinPeak 2 285W 3S-3P 2.6kW-STC 1.9kW-NMOT Array
    MN Solar Classic 150 / Conext SW 4024 Inverter latest firmware
    Trojan L16H-AC 435Ah bank 4S connected to Inverter with 10' of 4/0 cable / 24 volt system
    Grid-Assist Off-Grid / Need 3200Whs Daily
    System, Pics and Discussion