Crazy Voltages to AC Input from Generators
Hi, new here, glad to be here!
I posted this on another forum, but still needing help, input or insight on this.
I am new to the Solar Power System world but I have a remote Swamp Camp and I had some money saved so I thought I would buy a System because parts of the year no AC is needed. I got this system http://www.solarpenny.com/Magnum-Ene...assic-(4p).htm in the 4024 Version. I have 4, 6 volt Trojan L16 RE-B for my storage.
Now I have 2 Generators at my Camp. A Westerbeke 4.5 KW and an Onan DJE 6.0 KW. I like redundancy
Both of these Gensets run fine and produce at 60 HZ, and 122-124 volts
I know Generators very well, and I am no novice when it comes to electrical connections.
Now the Crazy part. When I have the Westerbeke connected with out the AC Input Breakers on I read the voltage in the panel at AC In and it is 122-124 volts. I flip the breakers on the panel it bogs down the Genset, and the voltage rises up to 160 volts or so and the breaker trips. I see the Charging light come on with this Genset connected.
Now when I have the Onan connected it does the exact opposite. A good 122-124 volts at the AC In, flip the breakers on the panel it does not bog down the Genset and it drops to 8-5-9.6 volts. I do not see the Charging light come on with this Genset.
I set the AC input Amps in the Inverter Controller to 15. The Westerbeke puts out 19 each leg and the Onan 25 so I thought that would be a good start for that setting.
Not sure if anyone has ever saw this type thing, or have any ideas, but they are all appreciated
I have since been to my Camp and I isolated it from the System. I get the exact readings mentioned here as I did the first time around, so it has to be in the System I bought.
I want to add that both of these Gensets run my Camp with no issues, and it appears the Solar System itself works fine in running things in my Camp.
Thom
South of New Orleans
Thom
0
How does the solar system work? what is the interface between the two AC systems, bypass switch? or lockout ?
I woulds suspect a short / bad connection somewhere. Did you use a torque-screwdriver?
All connections made with a hydraulic crimper, fitting is attached have heat shrink?
hth
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge, Hughes1100 Sat Modem
I am measuring the Gensets with no load, just seeing what they were out putting to the AC Input locations in the panel.
I bought the System pre-assembled as far as the Panel, Inverter, the inverter remote controller, and the Solar Charge Controller. They came mounted on a board as one. It does show they used heat shrink, not sure on the torque screw driver, but possibly. I myself do not own one, but always ensure I make good tight connections when I wire up things to a panel.
The System has one ground for the Camp and the Solar System. I un-bonded the neutrals on the Gensets and have just one neutral to ground bond for the entire system. The Gensets are connected to the entire system grounding point through the wiring panel, as is everything else.
Both the Solar System, and Generators work fine independently. I can look through and see what pics I have of the box internals if that would help, but as it came, they were clearly labeled.
Thanks again. I am not a wuss so if you think I got something wrong, let me know. My goal is to have this working correctly and get all of the features I paid for!!!!
I'm sort of wondering if the inverter is set up for 120/240 split phase input, and the gennies are wired for 120v single phase output, or maybe vice-versa.
Inside the box there are 2 AC Input a Neutral, Ground. AC Out has 2 AC Out connections, the neutral and ground are used by both. It looks like this inside (See Link to pdf) but with 2 #18 for AC IN, and 2 #@0s for AC Out. http://www.midnitesolar.com/pdfs/classic_simple_flow_diagram.pdf
Thanks for all of the extra sets of eyes on this!!!