I have 5 of these (battery)
And 3 0f these (panel)
http://www.pro-umwelt.de/solarmodul-kc-158g2-158wp-p-103.html?language=en
Was thinking of a mobile power station on a trailer
I have a fair bit of electrical experience but could really use some suggestions on where to go with the charge controller ,inverter and anything else I might need.also interested in bussing configuration for the batteries Thanks
WB-LYP260AHA LiFeYPO4 (3.2V/260Ah)
https://www.ev-power.eu/Winston-40Ah-200Ah/WB-LYP260AHA-LiFeYPO4-3-2V-260Ah.htmlAnd 3 0f these (panel)
You can wire four of your batteries in series to get a single 12V string. Depending on your charge controller, and the voltage range of your inverter, you might utilize all 5. The specifications for the batteries say their minimum voltage is 2.5V, so 5 in series would be a minimum of 12.5V. The problem would be the inverter. Most 12V inverters have a max voltage of 16.0-16.8VDC, and 5 in series would need to charge at 19.0VDC, higher than the inverter's limit. So, you're likely to be stuck with one extra battery.
You can wire your three panels in series if you use an MPPT controller. The 70VDC output needs to be transformed down to 15.2VDC by the controller, which would give you ~30A charging under perfect conditions, or maybe ~24A under routine conditions. That works out to be about C/11 in the real world. This Renogy MPPT will work for you. https://www.renogy.com/renogy-40-amp-commander-mppt-solar-charge-controller-w-mt-50-back-order/
You can pair it with this Sine Wave inverter https://ressupply.com/inverters/samlex-pst-1000-12-pure-sine-wave-inverter
Note that it's max voltage is 16.5, so that means only 4 batteries in series. You'll need to connect this inverter to your battery string with very heavy copper cables, 2/0 or 4/0.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop)
- 244 Forum & Website