Charging a battery

Options
kau
kau Registered Users Posts: 8 ✭✭
Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.

Comments

  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,044 ✭✭✭✭✭
    edited January 2017 #2
    Options
    If your panel has 36 cells it would be a 12 volt nominal panel. When connected to the battery you will notice the voltage output drop to somewhere below 14.4 volts depending on the state of charge of the battery. You can crudely charge your battery by monitoring the voltage but to do it properly you need a charge controller to do the absorb phase which holds the voltage steady at a predetermined voltage and allowing amperage to flow and complete the charge cycle . After absorb the controller will go into float and maintain your battery at 100% full until your battery loads pull it below full at which time the charging cycle begins again, provided there is sun, Ie; the next day. 

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric,  460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.

  • oil pan 4
    oil pan 4 Solar Expert Posts: 767 ✭✭✭✭
    Options
    The short answer:
    No.

    Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.

    Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    If you check every 15 minutes, log when the battery is at the proper absorb voltage, and disconnect before you cook the battery, it's easier to get a charge controller, unless this is a one time thing.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Marc Kurth
    Marc Kurth Solar Expert Posts: 1,144 ✭✭✭✭
    Options
    kau said:
    Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
    Depending upon the size of the battery (or batteries) and what/when the load profile looks like - you may have no risk of overcharging at all - or you can cook it rather quickly. It's like asking: "How long is a piece of string?"  Well, it depends............

    Generally, it is never a good plan to feed batteries uncontrolled voltages.

    Marc
    I always have more questions than answers. That's the nature of life.
  • kau
    kau Registered Users Posts: 8 ✭✭
    Options
    If your panel has 36 cells it would be a 12 volt nominal panel. When connected to the battery you will notice the voltage output drop to somewhere below 14.4 volts depending on the state of charge of the battery. You can crudely charge your battery by monitoring the voltage but to do it properly you need a charge controller to do the absorb phase which holds the voltage steady at a predetermined voltage and allowing amperage to flow and complete the charge cycle . After absorb the controller will go into float and maintain your battery at 100% full until your battery loads pull it below full at which time the charging cycle begins again, provided there is sun, Ie; the next day. 
    Thanks little, my cc croaked

  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,044 ✭✭✭✭✭
    Options
    Kau,  your welcome. Apparently the description wasn't necessary. Sounded from your opening post in the solar beginners corner you might not have done this before.

    2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old  but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric,  460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Options
    You will also want to keep an eye on temps as voltage reaches absorb. You might be able to do a sort of crude PWM absorb by connecting and disconnecting the panel.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • PNjunction
    PNjunction Solar Expert Posts: 762 ✭✭✭
    edited January 2017 #9
    Options
    Heh, actually you will undercharge if you just pull the panel off the battery when it reaches say 14.4v and you have an eagle-eye on your voltmeter.  However, If you leave it connected, the voltage of the battery will eventually try to reach the voltage of the panel, about 18v for a nominal 12v panel, and you will quickly kill it.

    In a total pinch on a deserted island, this technique might be enough to start your vehicle, even though it is not fully charged.

    If you use the eagle-eye voltmeter monitoring method, you'd have to emulate the old style ping-pong hysteresis controllers.  That is, let the terminal voltage rise to say 14.4v, pull the panel, and then let it rest until the voltage of the battery drops to 13.2v.  Re-attach the panel, and once again remove it when the voltage is 14.4v.  Rinse and repeat hundreds of times.  Each cycle of this gets quicker and quicker.  Take a phone call, turn around, and you are cooking your battery with high voltage.

    Even if you DO have a "hysteresis" type controller (such as cheap HF, Coleman, Sunforce 7a types), hysteresis charging is VERY inefficient and was common back in the 1970's.

    In other words, unless you are on a deserted island with nothing but a panel, voltmeter, time on your hands, and a battery, get yourself a solar controller - pwm at least. :)

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Options
    @PNjunction - that's pretty much the crude PWM I had in mind. Note OP said his cc "croaked". I assume he wasn't talking about a sound it made :-)
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • mvas
    mvas Registered Users Posts: 395 ✭✭✭
    Options
    kau said:
    Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
    At what voltage, do you think, the battery would be 100% fully charged
    when attached to the 70 Watt solar panel and in the full sun ?

    It really depends upon the size of the battery, in Amp-Hours.

    A typical 100 AH wet battery would reach 15 Volts @ 4.6 amps and will be about ~95% recharged.
    The above describes a typical Bulk Charge.
    At this point, we would normally switch to a constant 15 Volts ABSORB, to taper the amps until 100% recharged.
    But that is not going to happen if you leave the battery connected to the Solar Panel.

    So at this point, if you do leave the Solar Panel connected ...
    You would only need about another 5 AH ( 100 AH battery x 5% remaining )
    That means another ~1 hour (max) of charging at 4.6 amps.
    That would push the final voltage near 16 volts !

    I would disconnect the solar panel from the battery when either:
    a) The battery reaches 16 volts @ 4.3 amps or
    b) one hour has passed since the 15 volt reading
    which ever occurs first.
    The battery will be very near 100% recharged.

    Voltages at 70° F.
    Measuring the SG and reading no increase is the best way to know 100% recharged.

  • stranger
    stranger Registered Users Posts: 22 ✭✭
    edited February 2017 #12
    Options
    How about a potentiometer in the circuit to give a specific voltage drop, to regulate the voltage after absorb voltage is achieved?

    Okay, a high-power pot could be expensive. What other kind of variable load would be appropriate in a pinch?

    Edit: I was thinking potentiometer, not variac
  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    Options
    I would get a cheap 10A charge controller  <$15, and call it a day, there are better things to do with time, unless you're locked up in jail somwhere.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • stranger
    stranger Registered Users Posts: 22 ✭✭
    Options
    > @mcgivor said:
    > I would get a cheap 10A charge controller  <$15, and call it a day, there are better things to do with time, unless you're locked up in jail somwhere.

    Oh, no doubt. A charge controller is the way to go. I was trying to think outside of the box, MacGyver-style. There have been a couple of winter days that my battery bank was in dire need of a charge and there was no propane for the generator, because the weather kept me from driving the 8 miles of mud to get to town 20 miles away. Pop the hood. Hook up the jumper cables to the inverter to power the battery charger. Yeah, the battery charger was underpowered, but it got me through the day. I would have jumped it all the way to the battery, but my cables weren't long enough.
  • stranger
    stranger Registered Users Posts: 22 ✭✭
    Options
    Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
  • kau
    kau Registered Users Posts: 8 ✭✭
    Options
    kau said:
    Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
    Depending upon the size of the battery (or batteries) and what/when the load profile looks like - you may have no risk of overcharging at all - or you can cook it rather quickly. It's like asking: "How long is a piece of string?"  Well, it depends............

    Generally, it is never a good plan to feed batteries uncontrolled voltages.

    Marc



  • kau
    kau Registered Users Posts: 8 ✭✭
    Options
    stranger said:
    Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
    Thanks everyone for the feedback, I am getting use using this forum, seems to be set up quirky, anyhow, I decided to keep the battery up with a generator and a charger(quik charge at 15 amps), I know this isn't the best way. I use the battery once a week to run a 12volt pump to water gardens. I don't seem to be able to edit my post.:( Do other have trouble on this forum? As I was trying to say, I will be installing a charge controller for that set up. I would like to change the subject, I will start another thread. Thanks again!
  • BB.
    BB. Super Moderators, Administrators Posts: 33,440 admin
    Options
    You should be able to edit your post up to 1 week after it has been posted... There should be a little black "gear" in the upper right of the box around your post... Click on that and you should see Edit/Delete.

    If you need to change something later--Just send me a PM and I can take care of it.

    -Bill "moderator" B.
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    edited February 2017 #19
    Options
    and you have to click on that option too, "EDIT 1 week" is a bit of a misleading statement...
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • archsabino
    archsabino Registered Users Posts: 4
    Options
    Hi Kau,

    Thanks for this query. A panel with 36 cells means that it's a 12 volt nominal panel. If you connect the battery, your voltage output might drop. Well, sure you can charge it, but you're going to have to monitor the voltage. It'll have to go through the absorb phase wherein you'll need to have a charge controller.

    Thanks,
    Archsabino
  • Johann
    Johann Solar Expert Posts: 245 ✭✭✭
    Options
    kau said:
    stranger said:
    Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
    Thanks everyone for the feedback, I am getting use using this forum, seems to be set up quirky, anyhow, I decided to keep the battery up with a generator and a charger(quik charge at 15 amps), I know this isn't the best way. I use the battery once a week to run a 12volt pump to water gardens. I don't seem to be able to edit my post.:( Do other have trouble on this forum? As I was trying to say, I will be installing a charge controller for that set up. I would like to change the subject, I will start another thread. Thanks again!
    Could had used a 25 watt 12 volt automotive bulb in series with the panel  to charge with about 2 amps or a automotive high-beam bulb to charge with about 4 amps. It could had charged the batteries slower to keep it alive, but there may be still a need to monitor and disconnect the battery.
    But at the end, the amps needed to be used depends on the size of the battery size.