Splicing #16 AWG to a #4 AWG
The solution that I've come up with is to strip an 1/8" of the insulation from the #4, strip and wrap the #16 around the #4, make a mechanical connection and then apply solder.
Is this an OK solution? Or is there a better one?
Thanks.
how about a using a screw-type bus-bar block with various sized holes... scew the #16 in a small hole then a #4 in a bigger hole, then a #4 jumper going to your box/component..
~1.5Kw PV in parallel
Morningstar MPPT-60 controllers (2) in parallel
3 Trojan tr-1275's in parallel 450ah total
Samlex 2,000 watt 12-volt inverter hardwired -
cupcake said:how about a using a screw-type bus-bar block with various sized holes... scew the #16 in a small hole then a #4 in a bigger hole, then a #4 jumper going to your box/component..
Thanks. Although the #4 PV-in wire passes thru the box, it is not cut in the box. In fact, the only reason its there at all is to connect to #16 from the surge protector, which is attached to a knock-out.
geoffleach said:I'm installing a MidNite surge protector on the box that carries the PV-in disconnect. The neutral wire runs thru the box (i.e., its not broken in the box.) I need to attach the #16 wire from the surge protector to the #4 PV-in. I could use a split-bolt for this, but that seems clumsy, not to mention taking up space in a small box.
bill von novak said:geoffleach said:I'm installing a MidNite surge protector on the box that carries the PV-in disconnect. The neutral wire runs thru the box (i.e., its not broken in the box.) I need to attach the #16 wire from the surge protector to the #4 PV-in. I could use a split-bolt for this, but that seems clumsy, not to mention taking up space in a small box.
Believe that the SPD uses #16 AWG wire ... at least implied.Stripping the #4 cable, and wrapping the stripped #16 around it, is not a very good approach.
How about one of these:
https://www.solar-electric.com/insulated-terminal-bus-bar-short-black.htmlBelieve that the speced minimum wire diameter is 14 AWG, although, you might be able to get away with folding back the bare wire on itself, under a small screw position in the busbar, and probably be OK.
Often, PV SPDs are mounted in the Combiner, and a breaker is used as the connection point for the PV positive side PV connection for the SPD ... some Combiners do not have room for the additional breaker, especially when doing an SPD retrofit.
If this addition will need inspection, adding things like busbars and an SPD, might not pass inspection ... it all depends.
Just my opinion, FWIW, Vic
Thewire is provided by teh surge protector, so it should be OK.
Vic said:bill von novak said:geoffleach said:I'm installing a MidNite surge protector on the box that carries the PV-in disconnect. The neutral wire runs thru the box (i.e., its not broken in the box.) I need to attach the #16 wire from the surge protector to the #4 PV-in. I could use a split-bolt for this, but that seems clumsy, not to mention taking up space in a small box.
you should be able to jam all that into the big baby box... I got me one... there's room...
- 244 Forum & Website
- 653 Solar Water Pumping
- 628 Discussion Forums/Café
