Hi, Ive just been studying the install guide for the new XW60 MPPT charge controler and it shows and makes a point of wiring the negative output from the controller directly to the -ve battery terminal. No problem, however it goes on to say (Do not connect the battery negative to ground) The wiring diagram does not show the balance of systems like the inverter and disconnect. Which in my case is a SW3024E and Dc250 disconnect in which the negative lead from the battery bank goes to the bonding block in the disconnect which as per Xantrex instructions is bonded to earth thus means that the battery -ve is earthed or grounded. Please explain what is right I already have 2 C40s in the system and they have there -ve output direct to the bonding block, which conects to the negative -ve battery terminal. The manual also states to earth the battery terminal metal box enclosure, which is fine except my enclosure is made of concrete and insulated with high density foam.
Back to Top

rm solar
Senior Member



Joined: 04 June 2004
Location: United States
Online Status: Online
Posts: 61 Posted: 07 August 2007 at 6:12pm | IP Logged


basically the xw60 has a ground fault built in so it does the bonding for you i believe
Back to Top

eyedid
Moderator



Joined: 29 June 2007
Online Status: Offline
Posts: 8 Posted: 08 August 2007 at 9:20pm | IP Logged


Rm solar is right. The XW MPPT chargers integrate a GFP. Connecting battery negative to ground disables the PV GFP.
Back to Top

nigtomdaw
Member



Joined: 06 November 2006
Online Status: Online
Posts: 23 Posted: 08 August 2007 at 11:12pm | IP Logged


Ok but my -ve battery terminal is effectively grounded in the bonding block on the Xantrex disconnect as you recommend !That was my concern ! Is this a problem ? or is it that this doesnt affect the XW because of its -ve output main current carrying wire direct to the -ve terminal of the battery..
There,,,,,, thats as clear as mud !

Comments

  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Options
    Re: Niel as reested

    you should ask xantrex of this for i did not help to design it, i don't have their equipment to say from experience, and i'm not employed by xantrex either. and btw, what is reested?
  • boB
    boB Solar Expert Posts: 1,030 ✭✭✭✭
    Options
    Re: Niel as reested

    Did you see that the GFP is just a fuse from negative to chassis ? This is
    evidently also what Xantrex does in the GT3.0 I think.
    It works at least and it's pretty cheap, as far as added parts cost to the
    unit goes.

    boB