Typically, what equipment is used with the Air 40? From a DC disconnect on the tower to a some kind of turbine control and dump load. The turbine puts out 48 VDC, can it be connected directly to a charge controller? Thanks.

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,433 admin
    Re: Primus Air 40

    Sorry, have to go right now...

    Have you taken a look at the manuals (our host, NAWS, has them online):

    Primus Wind Power AIR 40 Specifications
    Primus Wind Power AIR 40 User Manual

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Re: Primus Air 40
    Typically, what equipment is used with the Air 40? From a DC disconnect on the tower to a some kind of turbine control and dump load. The turbine puts out 48 VDC, can it be connected directly to a charge controller? Thanks.
    It can be connected to a CC designed or set up for wind turbine use. There has to be some sort of dump load either controlled by the CC itself or controlled separately like by the Midnite Solar Clipper. And the CC should be MPPT with a conservative Vmax.