Combining differing Series Arrays

westbranchwestbranch Posts: 4,111Solar Expert ✭✭✭✭
I have 4 Mitsubishi 120W panels 17.6V Vmp, 22.0V Voc, 6.84A Imp, 7.36A Isc ...

I located some Luxen 130W panels 17.6V Vmp, 21.6V Voc, 7.39A Imp, 8.69A Isc

I plan on 4 series panels per array with 3 arrays in parallel, 12 panels per CC, 2CC's.

so there would be 1 array of Mits. and 2 of Luxen's on one of the CC's.

The Mits. Array = 70.4V Vmp, 88.0V Voc, 6.84A Imp, 7.36A Isc
the Luxen array = 70.4V Vmp, 86.4V Voc, 7.39A Imp, 8.69A Isc....no problems here so far, each array is 4 in series and they are all matched panels

But what happens when the array outputs are combined? the Vmp's match but the Imp does not?
Will the lower Imp be what the CC 'sees'?:cry:

Should I reassign the 4 Mitsubishi panels to another job?
 
CL 647 asleep  24V 900Ah C&D AGM
CL29032 FW 2079/ 2073/ 2054 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
Linksys Wet54g WiFi Bridge ,  ASUS RTN10 router, Hughes1100 Sat Modem
Omnicharge 3024, Cotek ST1500W 24V Inverter,
1680W & E-Panel/WBjr to come, Eu3000i & 1000i Gens,
West Chilcotin, BC, Canada

Comments

  • CariboocootCariboocoot Posts: 17,615Banned
    Re: Combining differing Series Arrays

    No worries. The Imp only matters in the series connection, just as the Vmp only matters in the parallel one.
    So four of the Mitsu's in one string and four of the Luxen's in another one or two will be fine. The Imp's aren't that far apart here either. If it was a really big difference, fuses would prevent the higher current panels from frying the lower ones if something should go wrong.