Interpritation needed
Fe-Wood
Solar Expert Posts: 96 ✭✭
So I'm looking at the charging chart from Crown Batteries for my specific batteries and trying to adjust my Magnum Energy Inverter Charger and have some interpretation questions.
*Is Constant Current Charging the same as Bulk Charging or Absorb Charging?
*Is Charge Factor the same as Charge Efficiency?
Reading the 2 manuals is like reading Italian and spanish...
How do I obtain the Per Cell Voltage? I'm assuming I stick the positive test leed into one cell and the negative leed into the next one?
Thanks fort he help-
Re: Interpritation needed
Bulk is constant current charging.
Absorb and float are constant voltage charging.
Instead of a chart of 12/24/48 volt set of charts, they just give you volt per cell numbers and you multiply by 6/12/24 series connected cells for the bank charging voltages and temperature offsets.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Bill!
I didn't ask my question about the per cell voltage right- I want to know how to test the batteries themselves- each cell. -
Re: Interpritation neededI want to know how to test the batteries themselves- each cell.
To check battery state of charge, or for a possible bad cell, check the electrolyte SG. If the SG of all cells is not equal, then if it's a flooded battery, do an EQ, then check SG again. A bad cell will show up with bad SG. -
Don't expect every cell to read the same. The distribution of materials (lead and H2SO4) make for small variations from cell to cell. At least that's been my experience.
Ralph