Inverter Startup Question
miscrms
Registered Users Posts: 15 ✭✭
Can anyone verify this for me?
I'm looking at a Sunny Boy SMA5000US. The MPP tracking Voltage goes down to 250V, but the startup voltage is listed as 300V. I'm assuming that the array output will be near N*Voc until it passes 300V, then the inverter will fire up and the array output will drop to roughly N*Vmp. Is that about right?
For 12x2 CS6P-230P panels in Phoenix, I'm calculating my "hot" Voc should be ~374V, and "hot" Vmp should be at least 277V. Does that sound ok for the above inverter specs?
Thanks,
Rob
Thanks,
Rob
Re: Inverter Startup Question
Rob,
Since none of here (that I know of) work for SMA--You probably should give them a call and confirm your proposed configuration...
There have been times when the on-line tools have given wrong information, and other times when vendors have "proprietary" information on the operation of their product that they will not release (or even read it themselves:roll:).
At least you have the understanding of their product and how solar panels work (and are affected by temperature), so you should be able to get a clear and accurate response from the help line.
Ok, thanks very much! -
I have a Sunpower 6000US inverter, same exact as yours except slightler higher capacity, and the inverter will try to tie to the grid at 300 volts DC input. Once it does, it will bring down the DC voltage of the panel to near 250 volts. -
Re: Inverter Startup QuestionCan anyone verify this for me?
I'm looking at a Sunny Boy SMA5000US. The MPP tracking Voltage goes down to 250V, but the startup voltage is listed as 300V. I'm assuming that the array output will be near N*Voc until it passes 300V, then the inverter will fire up and the array output will drop to roughly N*Vmp. Is that about right? -
Ok, thanks!
Here's what I'm calculating:
Case 1) Max Startup Voc, cell temp = record low -2C
12 * (36.8 + (-27 * -0.34)% ) = 482.1 V (Inverter max = 600V)
Case 2) Min Startup Voc, cell temp = record high 50C + 20C freestanding rise
12 * (36.8 + (+45 * -0.34)% ) = 374.0 V (Inverter startup = 300V)
Case 3) Max Vmp, cell temp = record low -2C
12 * (29.6 + (-27 * -0.43)% ) = 396.4 V (Inverter Vmp max = 480V)
Case 4) Min Vmp, cell temp = record high 50C + 20C freestanding rise
12 * (29.6 + (+45 * -0.43)% ) = 286.5 V (Inverter Vmp min = 250V)
If those calcs look reasonable, it seems like I should be fine!
Panel Specs (CS6P-230P):
Voc = 36.8V
Vmp = 29.6V
TCvoc = -0.34% / degC
TCpmax = -0.43% / degC
Rob
- 628 Discussion Forums/Café