Fusing for small grid tie system
I am installing a small grid-tied system, (5) 220W modules and a 1.1kW Grid-tied inverter. I was curious if anyone had experience or comments on using in-line fuses for the single PV string rather than something like a Midnite Solar MNPV3 and whether it would meet code. Installation is on the side of a building with a very clean looking install. DC disconnect is on the inverter in the electrical room of the building. DC wire is run in metal conduit from exterior to DC disconnect.
This is my first post but I use this forum for information all the time and appreciate everyone's willingness to take the time to share their knowledge.
Thanks,
Jacob
    Re: Fusing for small grid tie system
    How will the panels be installed... 5 in parallel, or 5 in series? (or is this a micro inverter installation?)
    For one or two parallel strings, you do not need any series protection fuses/breakers in the solar array side. I think you still need a DC disconnect before it goes into the building (not a code guy).
    It also, somewhat, depends on where you live. The local building department/inspectors may also have their own requirements.
    ....It also, somewhat, depends on where you live. The local building department/inspectors may also have their own requirements...
    The DC disconnect shall be painted Puce with Endangered Tiger Orange stripes.
    The AC disconnect shall be painted with Emerald Red, with Gold Accents at the corners
    The Ground Rod shall be buried 7.9' and connnected with a fancy green & yellow stripe wire, no less than 6 gauge.