Will This Work ????????
Gregory J Barrett
Registered Users Posts: 5 ✭
Re: Will This Work ????????
It will work to provide 12VDC, if the 24 cells are all in series. Your sketch is oversimplified, and I'm not sure what it is showing with 8 rectangles ?
It won't recharge a battery though, you need about 15V at the terminals to recharge.
Are these planned, or already built ?
If already built, you need to use 2 in series and a MPPT charge controller to charge a 12V battery.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Each colem has eight .5 volt 4 watt cells connected in series ...
3 columns per pannel connected in parallel
five panels connected in series giving me 19 volts
Yes I have built and I thought parallel columns would give me more power. -
you are correct, cells in parallel add power. So you have 12W @ 4V each panel, 12w @ 16 v = .75A under perfect conditions.
32 cells in series = 16VWell, you may just barely be able to slowly charge a battery. I would remove all the diodes, except for the ones in one panel. You loose a volt across each diode. keep one set of diodes to prevent the battery from discharging at nightPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Cells are .5 volt 4 watt.... Each column has 32 watt....
3 colums in parallel each panle = 32 watt Right
now tie 4 panles (4 volts each) in seires = 16 volts ...32watt ???
It's just not charging my 4 12vdc batteries connected in parallel -
The basic math:
0.5 Volts * 8 = 4 Volts, 4 Watts * 8 = 32 Watts (8 Amps) each string ("column").
Times three strings; each panel is 4 Volts, 24 Amps, 96 Watts.
Four of these in series yields: 16 Volts, 24 Amps, 384 Watts.
But like Mike said to begin with: you won't charge a 12 Volt battery from 16 Volts (especially not if it's Voltage open circuit). A normal "12 Volt" panel has a Vmp of 17.5 - 18 Volts and a Voc of 20+.
Build another panel, put it in series, and get 20 Volts, 24 Amps, 480 Watts. -
Re: Will This Work ????????Gregory J Barrett wrote: »Each colem has eight .5 volt 4 watt cells connected in series ...
A later post shows 5 panels in series, not the 4 from the drawing...
5 panels will be Vmp-array~19-20 volts... A little "hot" for a simple PWM controller so your efficiency will be a bit less (maybe 10% less unless you install a MPPT type charge controller--way more expensive).
Nominally, 36 cells at ~17.5 volts is used for charging a 12 volt battery bank.
Nothing will be hurt/damaged by ~19.5 volt panels that I would expect.
Thanks You All for the help.
My controller is a Coleman Air diversion Controller
160amp -
? what is... Vmp...PWM....MPPT -
Re: Will This Work ????????Gregory J Barrett wrote: »? what is... Vmp...PWM....MPPT
PWM is Pulse Width Modulation.
MPPT is Maximum Power Point Tracking. -
Re: Will This Work ????????you are correct, cells in parallel add power.
A couple FAQs about charge controllers:
All About Charge Controllers
PWM are pulse width modulation--basically just an switch that is turned on and off (rapidly or slowly--depending on the design). Less expensive to design and manufacture and good where solar panels match battery bank voltage (Vmp ~ 17.5 volts for a 12 volt battery bank--really you need about 14.5 to 15.0 volts to charge/equalize a battery bank; plus Vmp falls as the panels get hot in the sun).
MPPT are maximum power point tracking controllers. They are a digital switching power supply between the solar panels and the battery bank. A MPPT controller can take high voltage/low current of a solar array and efficiently down convert it to low voltage/high current required to charge the battery bank.
With MPPT, you can use solar panels with other than standard Vmp ratings, and you can make a ~100 VDC Vmp array and use much smaller gauge wire from the array to the charge controller--Very nice for high power systems and/or longer wiring runs from array to battery shed. But, MPPT controllers are much more expensive (PWM are $50 to $150... MPPT are $300 to $600+).
You have a diversion controller that is typically used with Wind/Water Turbines. When the battery is "full", the diversion controller turns on to dump the extra energy to a heater bank or other load. Diversion controllers are used because turbines will over-speed if not always connected to a load (battery, heater, etc.).
Solar panels can be turned on and off without damage--And the "quality" of charging for batteries is actually much better than that with a diversion controller.
You would be much better off using a series solar charge controller to charge the battery bank than a diversion. Solar Chargers will quickly charge and maintain the charge more accurately than diversion type controllers.