Need help with my solar puzzle?
windgate32
Registered Users Posts: 8 ✭✭
Ok, here goes,
Before I get the spanking I rightly deserve let me say I know I have tried to do this as far backwards as possible, but hopefully at this point it is salvageable. This is for an off grid cabin that has access to utility. A very kind fellow helped me out on here when I was already knee deep and helped clear out a couple things, TY btw again. I am going to throw it all on the table and if any of you like a challenge please help lol. My goal is to run a chest freezer,110v, 12v led light system, battery charging of items, cordless drill, batteries etc, some kitchen items, computer and printer including modem, small radio, fans. Most all of this would not be run at the same time. Then as I progress see how much I can and cant use.
The pieces….
(3) Sun hs-180-rl 180 watts, 32.60 Voc, 7.78 Isc, 25.9 Vmp, 6.95 imp
(2) Sun-120wp 120 watts, 21 voc, 8.23 isc, 16.80 vmp, 7.15imp
(1) Delta LA602 DC Lightning arrestor
(1) ETQ Generator 7250-8250 max watts
(2) 10 amp deep cycle charger for 6/12v, of course runs off of 110v.
(1) FM-80 Outback charge controller
and now the wrench in my plans…
(1) Sun SL-2012 Inverter see specs here http://sunelec.com/index.php?main_page=product_info&cPath=6_40&products_id=790
The questions….
First and foremost, should I try to return the inverter? May not be possible.
With all the other gear do I need a battery meter/monitor? Or will the fm80 take care of my needs there?
Based on the pv power I have currently, what is the largest battery bank I should use, using T-605 210ah at 20hrs, 105mins at 75amps 6v.
Based upon the pv’s I have, what configuration will be best as well?
I am sure I have forgotten something and will have other questions, ty in advance for any and all advice.
Sincerely, Randy
The pieces….
The questions….
Sincerely, Randy
Re: Need help with my solar puzzle?Based upon the pv’s I have, what configuration will be best as well?
you need to get a handle on roughly what your loads will be and it is difficult for us to know what the wattages or time factors will be for each load. this will be a term in watt hours and once determined the best battery can be determined as the ah x 12v = wh and rearranging wh/12v = ah. now you'd want to double that ah figure so as to not deplete the batteries below 50% and your battery ah capacity shall always be at least 2x or greater than your load ah totals.
as to the pvs, they are differing at this point enough to warrant 2 separate controllers. as mikeo pointed out another pv could've worked to your advantage, but it could also have been a 120w pv as you can make a series string of a 180w pv and a 120w pv being the currents are near to each other. that would realize 3 strings totally. now i can't say if the capacity in pv will wind up matching your battery capacity either as you've yet to determine what that battery capacity shall be to match your loads, but it may not matter when you can back it up with a generator.
i'm not sure why it is you want to return the inverter. only you can determine if it fits your needs or want to return it.
battery monitors are nice to have, but they aren't mandatory. -
Ty for the replies!
OK, no need for the battery monitor, that is a cost savings and is good. 8) Dang, ok being that they must be bought in atleast pairs, i can save and buy3 more 120w, but i want the highest IMP number correct? not watts?
I did buy the killowatt meter. I used it on my upright freezer, and 2 of my fans, I am going to use it on my computer next.I am not sure how to use the numbers I get from it. I will be buying a newer freezer but lets use this one for now.
0.51 PF
60 Hz
224 VA
115WATT
1.84 AMP
121.7 VOLTS
64.98 KWH
558 HRS ELAPSED
RATE OF 0.125
TY, RANDY -
Re: Need help with my solar puzzle?windgate32 wrote: »I did buy the killowatt meter. I used it on my upright freezer, and 2 of my fans, I am going to use it on my computer next.I am not sure how to use the numbers I get from it. I will be buying a newer freezer but lets use this one for now.
Explanations:- 0.51 PF
For other devices (motors, electronics, etc.) they appear to take more current than they should. This extra current requires larger wires, generators, inverters, fuses than a pure Wattage calculation would appear to suggest.
The math:- Power = Voltage * Current (sort of true--but for AC power and taking the above into account, the true equation:)
- Power = Voltage * Current * Power Factor
- Power = VA * Power Factor
- Notice that PF ranges from 0.0 to 1.0, and that when PF=1.0, then V*A does equal Watts.
- 60 Hz (line frequency of your power--50Hz is a common standard elsewhere)
- 224 VA (Volt*Amps--what the wiring/inverter must be sized for)
- 115WATT (power--what "energy" your battery/PV panels must supply)
- 1.84 AMP (current at 1201.7 VAC)
- 121.7 VOLTS (and AC line voltage)
- Volt*Amps = VA = 121.7v * 1.84 amps = 223.928 VA
- VA reading from meter = 224 VA
- Power = Volts * Current * PF = 121.7v*1.84a*0.51PF= 114.2 Watts
- Watt reading form meter = 115 watts
- PF = Watts / VA = 115 watts / 224 VA = 0.513
- I=P/V=115 watts/121.7 volts = 0.94 amps
Battery power wise--however, your freezer is drawing only 115 watts when turned on.
Now, for your system, we need to know how much power in a 24 hour period your freezer draws... It is on perhaps 50% of the time (115 watts for 30 minutes and 0 watts for 30 minutes)--So the meter will take the Watts*Time to figure out how much energy you use in a day:- 64.98 KWH
- 558 HRS ELAPSED
- 64.98 kWH = 64,980 Watt*Hours for the time period measured.
- 64,980 Watt*Hours / 558 hours = 116.45 watts
Anyhow... Your 1 day (24 hour) power usage is:- 116.45 watts * 24 hours = 2795 WH per day = 2.795 kWH per day
- 2.795 kWH per day * 365.25 days per year = 1,021 kWH per year
Take a look through the Energy Star website. I find, in my weather, that my refrigerator and freezer use a bit less than the rated power usage.
And I assume you programmed in $0.125 per kWH as your electric rate:- RATE OF 0.125
- 1,021 kWH per year * $0.125 per kWH = $127.625 per year electric cost
good that you have a meter. you can use that to get a handle on what the kwh per day will look like for each item you wish to power. when you know all of the requirements per day then it can be worked backwards for pv requirements.
as to the pvs being in pairs none of us said that exactly. i said 3 180w pvs and 3 120w pvs is workable with 3 not being an even number pairs are associated with so more than 1 120w pv won't apply in my example. mikeo's example does not work out to having 1 180w pv to a 120w pv so it really is not pairing that is the right wording here. my example would however mean a series pairing of a 120w pv per 180w pv.
do not jump on the extra pvs just yet. work out your loads first and we'll figure for your batteries so put extra pvs, or the subject of the pvs, on the backburner until we address this first. -
TY for all the info. I am still trying to absorb it. 8) The freezer, yes is a frost free and, unfortunately is in our garage here in TX. I am sure that explains why it is running all the time. I really did not know this until now, so it is actually something I can fix and try to save some energy there. I am currently running the killowatt on my computer set up and I will experiment with the kitchen appliances and the tool, phone ipod chargers next. Thank you again for all the help and as soon as I get some more data I will be back. The money saved from the battery monitor and extra panel can be used for the batteries.
Sincerely, Randy
- 626 Discussion Forums/Café