MC4 connectors and amperage ratings

Options
westbranch
westbranch Solar Expert Posts: 5,183 ✭✭✭✭
I am looking into a new array of 12 to 16, 110/120 W panels, 12 V nominal and have seen various panels with MC4 connectors that are rated @ 20 and 30 A.

In sussing out the details of a new 24V system I started wondering about the connectors.
I reviewed the specs for "Multi Contact" brand MC4 connectors, and noted that their MC4 's are rated at 30 A, while other brands are rated 20A max.

I have narrowed the array down to either going 4 parallel strings with 3 in series or 3 parallel strings with 4 in series to stay well within the limits of the MX 60 CC. Exact distance in unknown so am using 120 Ft total distance from Panels to CC

So, while using 12 v panels (24 V battery), 3 or 4 on a string, where the Isc usually is in the 5 - 8 amps range, can any one tell me if/when the amperage would/ could exceed 20 A if the panels are in series.

I can see where there would be > 20 A after the combiner box but there is no need for MC connectors after 'entry to the box' as conventional wiring would be used to accommodate larger wire size.

thanks
Eric.
 
KID #51B  4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Re: MC4 connectors and amperage ratings

    One series string of 4, eight amp panels, will not exceed 8 amps (except when very bright light hits them, via cloud edge effect, or refelction from snow/ice/sand.

    Cold weather increases the panel voltage, Brightness increases the amps.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||