200A 240V Double Throw Transfer Switch

Options
ligwyd
ligwyd Registered Users Posts: 209 ✭✭
HI there. Does any one have a line on a decent priced 200A double throw transfer switch? Not sure yet if my JHA wants it to be fused or not.......

Looking to install before a Solark 15K, and would facilitate by-passing if there ever was a problem.

Hopefully would never need it, but maybe better to have and not need, than not have and need it?

Thoughts?

Comments

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,753 ✭✭✭✭✭✭
    Options
    NAZ ! Good people and support for the Store here.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • BB.
    BB. Super Moderators, Administrators Posts: 33,448 admin
    Options
    There are Circuit Breaker interlocks available for manual switching. Basically the interlock prevents both sets of breakers being turned on at the same time (here is one example):

    https://interlockkit.com/

    Different brands/models of breaker panels would require different "sheet metal kits".

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,753 ✭✭✭✭✭✭
    Options
    An Inspector would probably not be excited about any 200A double throw that was not listed with it's enclosure. Just saying...
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net