Does any one has experience charging a battery bank through Inverter/Charger using a generator.
I have a 12 volt, 1200Ah battery bank (12 *100Ah)  AGM  batteries. I will like to use a  7000kw
B&S gas generator to charge those batteries, using the 150A charger built in
my 12V Freedom SW3000 Inverter/Charger. Is that possible, what hurdles should I be aware of?
Any advise or comments will be appreciated. Thank you
  • 706jim706jim Posts: 211Solar Expert ✭✭✭
    edited August 2 #2
    I have an old Trace that I use for charging with a small generator. It works fine although I am unable to reach its full amperage due to the size of my generator. You will find that this is an expensive way to charge batteries if you try to get them to float. In your case, you are getting in theory 1.7Kw from the inverter but are doing this from an engine rated at approximately 10Kw. So running close to a gallon of fuel per hour you can see where I'm coming from.
    Island cottage solar system with 1400 watts of panels, Trace DR1524 MSW inverter, Trace C40 PWM controller 8 Trojan L16's. My 25th year.
  • EstragonEstragon Posts: 2,607Registered Users ✭✭✭✭
    edited August 2 #3
    150a is some pretty big current. Like @706jim said, a 7kw generator won't break a sweat running that, but you'll want some big wire (thumb size) between the inverter/charger and battery to handle, and proper DC fuse/breaker. Small wire + no fuse = the wire IS the fuse. :wink:
    Off-grid.
  • mcgivormcgivor Posts: 2,052Solar Expert ✭✭✭✭
    Personally I would be thinking of ballance during charging/dischargeing with that amount of parrallel batteries, how are they wired? Recommendations are generally 3 maximum parrallel battery strings, but 12, that's extreme.
  • BB.BB. Posts: 27,684Super Moderators admin
    Here is the background on wiring a number of parallel batteries together:
  • Marc KurthMarc Kurth Posts: 432Solar Expert ✭✭✭✭
    Yes, I do see this approach with large motor coaches with 100a to 150a inverter/chargers. Many of today's high end coaches run six to eight 12v batteries at 260 ah each, and custom "entertainer" rigs can run as many as (16) 12v batteries x 260 ah each. Yes, that's close to 50 kwh total, but that is split between two inverter/charger/battery bank sets.
    Generally, the larger systems are set up as 24v to get the current down to a manageable level. So, that's four to six parallel strings, occasionally more.
    Lifespan is generally 6-8 years for this application, unless the bus "lives" in the Southwest deserts - then 5 years, which happens to be the warranty period. Typical wiring is a pair of 4/0 for each leg of the main leads to and from the inverter/charger..
    The trick to making several parallel batteries (or strings of batteries) live a longer life, is to have LOTS of time in float. This is one of the reasons that many batteries in parallel should be avoided in off grid PV systems.
    Marc
    I always have more questions than answers. That's the nature of life.
  • mike95490mike95490 Posts: 7,790Solar Expert ✭✭✭✭
    I do it all the time in winter, just for long enough to get the batteries through Bulk and start Absorb.
  • jonrjonr Posts: 1,029Solar Expert ✭✭✭✭
    Note that the Smartguage site is completely wrong about "perfect balancing" - you will get much closer to that using an ammeter and wiring that may be quite different than what they show.    It also glosses over self balancing (a huge effect ignored in their calculations) and uses link resistance that is about 30x what 4/0 cable has (let alone bus bars).    That being said, method #3 makes individual fusing an option.