Breaker for generator battery.....will this work?
porch13porch13 Posts: 58Registered Users ✭✭✭
I have a 15KW Generac generator that is used for pumping water at a cabin.   Over time, the generator will slowly drain the battery.  I have a small panel and charge controller to charge the battery, but this time of year the sun is so far south that a tree blocks the panel.  To separate the battery from the generator when I'm not using it, I've thought about putting an in-line breaker on the positive battery cable.  Would this one fit the bill for that?:
https://www.solar-electric.com/mrcb-60-amp-dc-circuit-breaker.html
The generator calls for a battery with 350 CCA, but I don't know how that translates to what this breaker can handle.
Thanks much everyone!
Northern Arizona...4050 Watt off-grid system - Outback FP1 - Rolls 605 in a 48V bank
  • westbranchwestbranch Posts: 5,024Solar Expert ✭✭✭✭
    You did not tell us how often you start the genny..?   I am not sure about that CB, since it has to take the surge draw of that starter ...  Do you have a Clamp DC Amp meter to at least get the running draw?
    why don't you use an AC battery charger? Probably 10A max as it would  charge when the genny is running.... for 1/2 hr or more when pumping..?
    West Chilcotin, BC, Canada
  • mike95490mike95490 Posts: 7,657Solar Expert ✭✭✭✭
    A breaker will pop when you start the genset,  Use a automotive disconnect switch, they mount right on the battery terminal
  • mcgivormcgivor Posts: 1,780Registered Users ✭✭✭✭
    The breaker is not rated to handle the current a starter draws which will trip the breaker, an automotive battery isolation switch would be far superior.
  • EstragonEstragon Posts: 2,334Registered Users ✭✭✭✭
    Are you sure the generator draws the battery down over time? Is the draw down because the generator doesn't charge the start battery enough during a pump cycle, or because of generator electronics idle consumption, or because the battery sits around too long? It's also possible the partly shaded pv and/or controller self consumption is drawing power from the battery, not the generator.
    If the generator is drawing power when off, it may make sense to establish what it's drawing power for before installing a breaker (or switch) to cut DC power.
    If it could be something else, it may make sense to investigate those causes.
    I think there should already be a fuse or breaker in the generator - starting battery circuit, but I'm not sure opening it is going to solve the actual problem. IMHO, you need to define the problem properly first, then find the right solution.
    Off-grid.
  • SolarMusherSolarMusher Posts: 170Solar Expert ✭✭✭
    If you don't have an automatic start, just pull off the fuse on the controller board and it won't draw anything...
    Or install a 120vac line from your system to power the 120Vac built in charger to keep this battery full.
  • porch13porch13 Posts: 58Registered Users ✭✭✭
    Thanks for the feedback, guys.  I'm completely off grid and there is no AC near the well house.  During warmer months the generator runs about once a week to fill a 500 gallon holding tank, and only run about every six weeks in the winter.  I'll look into the automotive battery isolator.
    Is the generator Auto-Start ?  If so, it's the auto start circuit draining the battery, and if you isolate it, it wont auto-start
    The generator does have an auto start option, but I don't use it.
    But is it disconnected? If not the parasitic draw is still there... regardless of us
