Calb lifepo4 charge profiles and inverter settings
mahendramahendra Posts: 141Solar Expert ✭✭
Please recommend charge profiles for midnite classic and outback vfx 3648 for calb ca 180 ah .projected usage would not exceed 50% dod.
  • Raj174Raj174 Posts: 584Solar Expert ✭✭✭✭
    @mahendra
    I also have an LFP bank and a Midnite Classic controller. If you don't have one already, I suggest getting a Whiz Bang Jr.
    It integrates with the classic and is only about 50 dollars. It's very good battery monitor.
    For absorb, I have used settings between 54.8V and 55.2V with a float setting of 53.6V. I recommend the cells be top balanced. It is critical that the voltage of each cell be very close at the top of the charge. Let us know if you need assistance with that.
    Rick
    12 x 300W Renogy PV, MNE175DR-TR epanel modified, MN Classic 150, Outback Radian GS4048A, Mate3, 54.4V 207AH HI Power LiFePO4 no BMS, 4000W gen.
  • mahendramahendra Posts: 141Solar Expert ✭✭
    Thanks I do have a whizbang jr.But how do you controller or monitor for low voltage disconnect on the inverter side.
    @mahendra
    You may be able to use the AUX 1 port dry contact on the Classic set as a low battery disconnect to power the inverter off via the inverter on/off switch connection. On the Radian I have, it's a jumper on a control board. Set to always on, or a toggle can be installed.
    I didn't think of that when I set mine up, so I used a JLD404AH Intelligent Ampere Hour Meter with a large 48 volt contactor.
    Rick
  • EstragonEstragon Posts: 2,226Registered Users ✭✭✭✭
    It's a bit more involved, but I also plan to use a Raspberry Pi to poll Classic modbus registers, and disconnect large but non-essential loads (eg. pumps) at higher voltages than LBCO. As voltage drops, the rPi will open relays on progressively more important loads.
    This should help avoid hitting LBCO (and shutting everything down) at all. IIRC, my Outbacks have a switch port that can also be controlled by a simple relay, which could be flipped by the rPi as well, or by the Classic Aux port.
    Off-grid.
  • Dave AngeliniDave Angelini Posts: 3,636Solar Expert ✭✭✭✭
    The outback inverter already has LBCO right?  Don't let your loads get that big or wait that long to charge the battery :)
    Have some headroom in the design!  Easy to say this before :)
    E-mail [email protected]
    It does, but 48 volts is uncomfortably low for a 51.2 volt nominal LFP bank.
    edited January 22 #8
    So adjust it? The inverter has adjustable LBCO?
    Rick maybe the bank has one too many batteries and 48 is has high as LBCO will go?
    Seems like a battery design problem or is this an issue with Prismatics because of no BMS ? Typical LBCO is 44V and lights out!
    It would be nice if it the upper limit was above 48 volts. Of course, a 48 volt prismatic bank would have 15 cells and it would work fine with the inverter LBCO. Though it's always nice to have more storage. I like 16, then again 17 is good too. All can be done with no BMS, just have to innovate.
    Rick