Dear All,

I hope everyone is doing well. Actually, I'm not expert in PV systems.
I have Axpert MKS3000 inverter. connected to battery bank in PV system. The output voltage of the inverter is as following:

1- Phase-to-Neutral=230V.
2- Phase-to-earth=125V.
3- Neutral-to-earth=105V.

Could you please explain those results for me.

Thanks a lot

Comments

  • mcgivormcgivor Registered Users Posts: 1,280 ✭✭✭✭
    Do you have the neutral bonded to ground on the AC side?
      1500W, 6× Schutten 250W Poly panels , Schneider 150 60 CC, Schneider SW 2524 inverter, 8×T105 GC 24V nominal 

  • engineerjaberengineerjaber Registered Users Posts: 3
    mcgivor said:
    Do you have the neutral bonded to ground on the AC side?
    Dear mcgivor, 

    They are totally isolated. could you please explain more!!


  • engineerjaberengineerjaber Registered Users Posts: 3
    The user manual of the inverter is attached
  • mcgivormcgivor Registered Users Posts: 1,280 ✭✭✭✭
    The blue wire is the neutral, brown is the live, green and yellow is ground, blue and ground should be bonded at a single point, typically after the inverter, any other neutral bonding, such as, at a generator should be disconnected, there should be only one point of neutral/ground bonding, if you are unsure of what you are doing, I highly recommend getting someone who is qualified, to prevent damage to your equipment, giving advice remotely is not the best, hope you understand, as I'm unaware of your  abilities.
      1500W, 6× Schutten 250W Poly panels , Schneider 150 60 CC, Schneider SW 2524 inverter, 8×T105 GC 24V nominal 