Calculating circuit breaker size for 12 volt panels in paralell - Off Grid?
Troutbeat
Registered Users Posts: 2 ✭
hi. I have a few questions concerning the calculation of the DC circuit breaker to use as a cut off switch for a string of 12 V panels connected in parallel.
please note I have three 200 watt 12 volt panels that I intend to connect in paralell. The Isc rating for each panel is 11.89 amps. I have an inline fuse of 15 amps on each panel.
1. What is the formula for calculating the DC circuit breaker size that I intend to use as a cutoff switch?
2. If you use the ISC rating do you multiply the Isc rating for each solar panel? For example if the isc rating is 11.8 A and you have three panels wired in parallel do you multiply the isc rating by 3 (not including the buffer of 1.25 - 1.56)? For example would the formula be 11.89 Isc x 3 x 1.25 (or 1.56 depending on your Country's rules)
Since there are fuses for each panel there is no need to use a circuit breaker, a DC rated disconnect, 45A or higher, is all that would be required, probably less expensive too. Don't be tempted to use an AC disconnect in a DC application, arcing will result, I'm assuming this is a convenience disconnect local to the charge controller.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Assuming you're combining the three panels into a single pair of wires to the controller, and are sizing a breaker before the controller to use as a disconnect, it would be sized to protect that pair of wires.
Depending on the length of that wire, you may want to size it larger than strictly needed (in order to minimize voltage drop), in which case you could use a bigger breaker for the oversized wire if you wanted.Off-grid.
Thank you. all square on your info. Much appreciated.
For or my own self development, and knowledge, re my second question, when calculating DC Circuit breaker size for panels wired in paralell, do you multiply the Isc of all panels.Troutbeat said:2. If you use the ISC rating do you multiply the Isc rating for each solar panel? For example if the isc rating is 11.8 A and you have three panels wired in parallel do you multiply the isc rating by 3 (not including the buffer of 1.25 - 1.56)? For example would the formula be 11.89 Isc x 3 x 1.25 (or 1.56 depending on your Country's rules)
Troutbeat said:Thank you. all square on your info. Much appreciated.
Correct1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
I would use a CB 3x the size of the fuse the panels call for. if the sticker on the panels says 15A, then 45A should work (with the right size wire.)But now that you have a breaker and a box, why not just use that as your combiner and 2, 15A breakers and forget the fuses. You can switch a string in/out of the system and compare & troubleshoot.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||