Philippines Electrical lines - L1 / L2 / L3 ... why is there no NEUTRAL?
ChanChan Registered Users Posts: 45 ✭✭
Philippines Electrical lines - L1 / L2 / L3 ... why is there no NEUTRAL? is it normal for all lines in the Philippines to have an L1 / L2 / - SINGLE PHASE - L1 L2 L3 - 3PHASE... When I tested 1 line to ground ... input around 110v each lines...
  • BB.BB. Super Moderators Posts: 27,055 admin
    Here are the two common methods for dropping 3 phase power to and end customer (there are variations, but these are the basics):
    Image result for Philippines Electrical lines - L1 / L2 / L3
    The Neutral may or may not be brought out to the customer's power panel (if you need 120 VAC or not). It can be still grounded at the power pole transformer(s) to give you a reading to ground.
    What voltage did you read Line to Line?
  • dennis461dennis461 Registered Users Posts: 96 ✭✭
    Let's start with some basics.  If you are testing with a voltmeter, you may not be able to tell if you have single phase, two phase, or three phase.
    I've read where the Philippines has two different standards.
    Rural is two wire L-N, at 230 VAC single phase.
    Larger older cities are L1-L2 240VAC single phase with neutral center tap. (L1-N 120 VAC)
    However, the wall outlets are wired for 240 VAC.
    You will  most likely need a good electrician to check your location.
    Camden County, NJ, USA
    19 SW285 panels
    SE5000 inverter
    grid tied
  • jonrjonr Solar Expert Posts: 889 ✭✭✭✭
    If only 3 wires are supplied, then don't try to use the ground instead (even if it seems to present a voltage you want).  It's not a good enough conductor.  If you need 110-120V, other options would be to ask for a neutral wire or use a transformer.