Delay start on the AGS-N for diesel

Options
mrkelleysaid
mrkelleysaid Registered Users Posts: 12 ✭✭
Just wondering if there is a delay for glow pugs to heat a diesel in cold, IE closing the circuit for 20 secs then closing the start?? just a thought as shed temps will get -15. If not will have to man start..
Any thoughts or custom build switch??
"Don't take life too seriously...you'll never get out alive". E Hubbard...  Mag 4448/pt100 Off grid, Great north Woods land of peace.

Comments

  • mcgivor
    mcgivor Solar Expert Posts: 3,854 ✭✭✭✭✭✭
    edited March 2017 #2
    Options
    A time delay relay such as the one attached has many options, inputs types, voltages and so forth. They are extremely reliable and versatile, have used them extensively in industrial controls.
    A diesel backup generator in a grid system would conventionally have a block heater which negates the need for glow plugs. If you are without grid power the need to preheat with glow plugs would be essential at -15° F or C ???. Some diesels, direct injection type, don't have glow plugs but intake heating grids but essentially do the same job. At such low temperature it would be advisable to add to that a warm up cycle, so as not to run cold under load. If unheated the diesel fuel can gel especially at temperatures below -20°C with #1 winterized fuel, to add to that the start battery will loose capacity, the list goes on. What is it you propose to do? These are shots in the dark.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    IMO, any generator (or engine) benefits from a warm up cycle.    Oil just doesn't lubricate well below ~140F.  I'd also use synthetic oil with a wide viscosity range.

    http://carnut.com/ramblin/img212.gif

    I am available for custom hardware/firmware development

  • Estragon
    Estragon Registered Users Posts: 4,496 ✭✭✭✭✭
    Options
    I think Magnum AGS have a preheat relay for glow plugs, also warm-up and cool-down cycles.