Clarification on Amps from Sunny Island to Critical Loads Panel?

Options
midijeep
midijeep Registered Users Posts: 102 ✭✭✭
edited January 2017 in Solar Beginners Corner #1
I'm a little confused about what the electrician told me about my (1) SunnyBoy,  (1) Sunny Island, (1) Midnite Solar E-Panel & (1) Midnite Solar AutoFormercsetup.  I have a grid-tied battery backup system.
The electrician told me that with my PV set up that instead of getting the 56 amps possible from the Sunny Island to critical loads panel , I would only get half that, 28amps.  He said I need two Sunny islands to get the full 56 amps.  That doesn't make any sense to me.
Can someone explain why I would be getting only 28 amps to the critical loads panel?

Comments

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Options
    a few questions first....  Are you referring to the ~1500W available from the SI?
    What is your battery voltage?
    What voltage are you talking about for the 56Amps?
    How are you using the Auto-former.


     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • midijeep
    midijeep Registered Users Posts: 102 ✭✭✭
    Options
    Are you referring to the ~1500W available from the SI?  Not referring to the 1500 Watt outlet on the SunnyBoy

    What is your battery voltage? 48 volts

    What voltage are you talking about for the 56Amps?  This would be AC going to the critical loads panel, so I am assuming 240 because the Autoformer is used to make the SI (120 V) and Autoformer to 240 V.

    How are you using the Auto-former?  To bring the voltage up tp 240V.  The SI along is only 120V.

    The Sunny Island is capable of handing 56 amps. 
    I'm wondering if it is a limitation on the critical loads panel he installed?  He explained something about 2 sides to incoming power from the Sunny Island .  I can see the voltage being 120v on one leg and 120 volts on the other in the panel where the breakers are inserted.







  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    edited January 2017 #4
    Options
    So you want 56A at the Critical Loads panel.

    Is that when the grid is down?  To me that is when  those loads are CRITICAL... thus they would be limited to 1500W like a fridge and a few others.

    He is correct as 28A x 48 V = 1344W,  and it looks like he threw in a fudge factor to account for system losses and the fact that the battery would be about 53.4V when discharging...

    What loads have you declared Critical? Do you want to have to but another SI?

     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • midijeep
    midijeep Registered Users Posts: 102 ✭✭✭
    edited January 2017 #5
    Options
    So you want 56A at the Critical Loads panel.

    Is that when the grid is down?  To me that is when  those loads are CRITICAL... thus they would be limited to 1500W like a fridge and a few others.

    He is correct as 28A x 48 V = 1344W,  and it looks like he threw in a fudge factor to account for system losses and the fact that the battery would be about 53.4V when discharging...

    What loads have you declared Critical? Do you want to have to but another SI?

    Well the problem is the microwave (on high at 1500watts) everything else on the critical loads panels works great i.e.  refrigerator , lights and furnace blower motor (natural gas).  The microwave when turned on high (100% power) will stop and start.  I'm thinking the only way to use the microwave will be finding the power that allows the microwave to stay on without stopping and starting which will take longer to heat what ever I'm heating up.

    I thought about a small capacitor bank between the battery bank and Sunny Island but I don't know much about where to start.
    Maybe another solution may be a Microwave Oven with Inverter Technology?

    I don't have another SI but I thought the Autofromer was suppose to give me the voltage for 240 and amperage?

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Options
    the autoformer does give you 240V but at half the amperage on each leg of the feed.... still the same number of Watts...
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • midijeep
    midijeep Registered Users Posts: 102 ✭✭✭
    Options
    the autoformer does give you 240V but at half the amperage on each leg of the feed.... still the same number of Watts...
    Sounds like I will need to add another SI to get the amperage up?  But my initial plan was to have power to a few critical loads not the entire house,  Maybe I can experiment with a Microwave Oven with Inverter Technology and have an alternative source for cooking as another backup.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Unless you are thawing blood at a hospital, a microwave is not a critical load (in my opinion)
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • midijeep
    midijeep Registered Users Posts: 102 ✭✭✭
    Options
    mike95490 said:
    Unless you are thawing blood at a hospital, a microwave is not a critical load (in my opinion)
    Opinion noted.
  • Raj174
    Raj174 Solar Expert Posts: 795 ✭✭✭✭
    Options
    Another option might be to get yourself a 700 watt microwave for when the grid power is down. They are probably less than 60 bucks.
    4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
  • midijeep
    midijeep Registered Users Posts: 102 ✭✭✭
    edited February 2017 #11
    Options
    I wanted to come back and report what I did.  I bought a  microwave where the power level can be adjusted but the microwave works on full power with no problems.  It draws about 13 amps at ~ 1300watts at full power setting.