Guide for wire sizing from charge controller to battery bank?
softdown
Solar Expert Posts: 3,822 ✭✭✭✭
Ideas?
I could probably look this up. Like food, fresh is better?
go here 5 th item down http://forum.solar-electric.com/categories/solar-information-links-sources-event-announcements
westbranch said:
http://www.openoffice.org/ This worked fairly well....except for "chopping off" the numbers for line loss.
Thought I seen an easy chart in a solar book...once upon a time.
Southwire has mobile apps for voltage drop and conduit fill. Once on your smartphone or tablet they don't need an internet connection.Off-Grid in Terlingua, TX
5,000 watt array - 14 CS 370 watt modules. HZLA horizontal tracker. Schneider: XW6048NA+, Mini PDP, MPPT 80-600, SCP. 390ah LiFeP04 battery bank - 3 Discover AES 42-48-6650 48 volt 130ah LiFePO4 batteries -
Wheelman55 said:Southwire has mobile apps for voltage drop and conduit fill. Once on your smartphone or tablet they don't need an internet connection.
Voltage.................40volts Maximum voltage drop...................3 % Typically, 3% or less is the recommended level for efficient operation of equipment. Length of cable run.................16 feet Current at the end of cable run......................16 amps
Yielded this:Results
1 conductors per phase utilizing a #12 Copper conductor will limit the voltage drop to 2.23% or less when supplying 16.0 amps for 16 feet on a 40 volt system.For Engineering Information Only:20.0 Amps Rated ampacity of selected conductor1.9029 Ohms Resistance (Ohms per 1000 feet)0.054 Ohms Reactance (Ohms per 1000 feet)1.2000000000000002 volts maximum allowable voltage drop at 3%0.889. Actual voltage drop loss at 2.23% for the circuit0.9 Power Factor
I was inputting data for the final run from the combiner box to the charge controller. Guess I didn't need to install the 8awg yesterday after all.
Also feel like I failed to account for one or two things.
Looking on the bright side you'll have less than 1% voltage drop using the 8 awg.Off-Grid in Terlingua, TX
Wheelman55 said:Looking on the bright side you'll have less than 1% voltage drop using the 8 awg.