what do i need to protect my batteries from getting overdrawn?

Options
parkerkempf
parkerkempf Registered Users Posts: 1
So i'm running 400w of solar on my sprinter van roof to a 35a charge controller to two 6v T105's (in series and everything protected with appropriate inline fuses), from those batts im running a 2kw inverter (with an inline fuse as well) for AC things like charging phones, vitamix, coffee grinder, etc,

also, 

I have a bunch of DC things like fans, fridge, lights, and heaters (like 15 amps if its all going at once)
my plan is to have a fuse box close to the battery, but i dont want all those things to run all night and overdraw the batteries...what do i need to put in between the fuse box and the batteries to protect them from this?

thanks!

Comments

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    edited September 2016 #2
    Options
    If they are good Quality DC rated breakers, they can server as disconnects to kill all loads, even the one to the inverter... after the loads are off
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    I would consider this alarm.  But I don't see an automated disconnect.

    http://www.bogartengineering.com/products/trimetrics/

    I am available for custom hardware/firmware development

  • softdown
    softdown Solar Expert Posts: 3,821 ✭✭✭✭
    edited September 2016 #4
    Options
    I consider the ability to disconnect due to low voltage to be absolutely critical for battery preservation. The regular inverters shut down at 10.5 volts (terrible) or 10 volts (even worse). Batteries left at 10.5 volts may not be long for this world. I have killed several due to 10.5 voltage disconnect default setting.

    I was able to find some disconnects for 12 volt and 24 volt systems. Some have housing, some do not. Some are rated for 10 amps, others for 30 amps. What they all have in common, so far, is the belief that we must run small wires to our inverters. I might be able to fit  #8 AWG into the wiring receptacle but probably not without cutting some wires. All you can then do is minimize the distance between the inverter and low voltage disconnect. Or something along those lines.

    In the real world, most larger inverters employ #2 AWG, or better, to connect to batteries. At 12 volts and up to 15 amps/120 volt, you should use large inverter cabling. Like #2 or larger...fine stranded welding cable is very easy to work with.

    At this moment in time, this is a huge problem. I'm sure we have some expert$ with a viable solution. The expert$ sometimes are of the mind that solar enthusiasts must surely have access to a money tree.

    Don't ever let your batteries stay below ~11.5 volts for very long. The premium solar batteries are built to handle periodic low voltage but, then again, replacing them costs three times as much.

    I recommend an ~11.5 volt disconnect level. After killing a number of batteries, I consider myself moderately experienced in this area.
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    That is a lot of loads... For 2x 6 volt @ 200 AH batteries--I would suggest a ~2500 Watt maximum load (for reliable operation)--A 2,000 Watt AC inverter is probably going to suck those guys down too quickly to be of much use. A 2 kW inverter will take around:
    • 2,000 Watts * 1/0.85 inverter eff * 1/10.5 volts cutout = 224 Amps (worst case, maximum 2 kW load)
    That is a lot for that small of battery bank. And a 400 Watt array will not supply that much energy. Say ~4 hours of sun (decently sunny area minimum for 9 months of the year):
    • 400 Watts * 0.52 typical off grid system eff * 4 hours of sun = 832 Watt*Hours of AC power per day (average minimum, excluding winter).
    That is about 20 minutes of 2kWatt inverter (running at full load) per relatively sunny day.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • South Africa
    South Africa Solar Expert Posts: 295 ✭✭✭
    Options
    I use a Victron battery monitor, where I set the SOC where I want loads switched off.

    Once it hits the set SOC, the BMV's internal relay is triggered.

    This little relay is used to trigger a larger AC relay to switch off all loads, connected to the inverter, I want off.
    5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied.


  • softdown
    softdown Solar Expert Posts: 3,821 ✭✭✭✭
    Options
    I use a Victron battery monitor, where I set the SOC where I want loads switched off.

    Once it hits the set SOC, the BMV's internal relay is triggered.

    This little relay is used to trigger a larger AC relay to switch off all loads, connected to the inverter, I want off.

    That looks like a nice solution and does have blocks to connect good sized lugs. At around $200 it is not cheap.
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • softdown
    softdown Solar Expert Posts: 3,821 ✭✭✭✭
    Options
    http://www.projecta.com.au/Products/DualBattery/LowVoltageDisconnects.aspx

    The shipping from Australia seems to be unavailable or prohibitive.
     
    Plus the disconnect points are too low or too high for my tastes.
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • South Africa
    South Africa Solar Expert Posts: 295 ✭✭✭
    Options
    Jip they are not cheap but here in SA a lot of us use them. Swapping on voltages just never worked for any of us.

    We change power sources between inverter and Utilities, powering a lot of devices in our houses, to save on batteries.

    We even wrote software using the data from BMV's to automate it all even more.

    But yes, they are expensive.


    5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied.


  • softdown
    softdown Solar Expert Posts: 3,821 ✭✭✭✭
    Options
    Interesting that Xantrex has several charge controllers that are much less expensive than their low voltage disconnects.
    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • softdown
    softdown Solar Expert Posts: 3,821 ✭✭✭✭
    Options
    It is not hard to find low voltage disconnects, some from reputable manufacturers such as: http://www.ebay.com/itm/BLUE-SEA-7635-M-LVD-LOW-VOLTAGE-DISCONNECT-/351836956899?hash=item51eb1de8e3:g:6jUAAOSwGtRX1cRO&vxp=mtr

    The vast majority are made to disconnect a single battery using small amounts of power. The trick seems to be finding disconnects that can handle ~#2 AWG cables and commensurate amperage draws.

    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • Johann
    Johann Solar Expert Posts: 245 ✭✭✭
    edited September 2016 #12
    Options
    softdown said:
    It is not hard to find low voltage disconnects, some from reputable manufacturers such as: http://www.ebay.com/itm/BLUE-SEA-7635-M-LVD-LOW-VOLTAGE-DISCONNECT-/351836956899?hash=item51eb1de8e3:g:6jUAAOSwGtRX1cRO&vxp=mtr

    The vast majority are made to disconnect a single battery using small amounts of power. The trick seems to be finding disconnects that can handle ~#2 AWG cables and commensurate amperage draws.

    My inverter got a build-in switch that can be turned off and on manually.
    So the trick would be that a low voltage disconnect device would turn the switch on and off at the inverter. So in reality, a low voltage disconnect device could be wired in parallel to that on-off switch at the inverter with very small wires like a #14 etc etc, just make sure that the internal switch/relay of the low voltage disconnect device is a '' dry '' switch ( no actual power coming out on that internal switch).  The # 2 wire would stay where it is.

    A while back I bought 2 of those and I used one for about 2-3 month as a temporary charge controller after my MPPT went up in smoke, just add a relay etc to up the amps you can switch. Something like that could turn other devices on or off depending on voltages of the batteries .

    I did not use/wire that ebay controller to control my inverter yet, but eventually I will get to do it.
    I have seen them for 24 volts and if I remember right I even seen one in a 48 volt version.
    if you look around, you even find them with a box/covers.