charge controller in ungrounded system

Options
carilchasens
carilchasens Registered Users Posts: 22 ✭✭
Battery bank is 12 volt, panels around 60 volts. Charge controller - I am looking at Midnite Classic - has negative connections for battery and PV as a common connection. So.. what is the effect, say, on battery chemistry, or whatever, of connecting ungrounded negative lines from the 12V battery and the 60V PV?

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Should be no problem.

    Most/Many solar charge controllers have a common connection for array negative and battery negative.

    Next question may be, should you chassis ground/earth ground the battery negative bus.

    Depends on where/how the system is installed.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • carilchasens
    carilchasens Registered Users Posts: 22 ✭✭
    edited June 2016 #3
    Options
    Bill, we have had ungrounded 12V DC for years. No motivation to ground, and the soil on our house flat is particularly rocky.