Breakers, Box, Charge Controller

Options
Zakarume
Zakarume Solar Expert Posts: 143 ✭✭
edited February 2016 in Solar Beginners Corner #1
As i have said before i am upgrading and redoing my battery bank. What i need to know is.
I have 2 Charge controller (Midnite classic 150 and Midnite Kid)
I want to run the wires from CC to batteries, but run them through the Midnite Baby Box. http://www.solar-electric.com/baby-box.html

1.Midnite classic 150. Is this a good breaker http://www.solar-electric.com/midnite-solar-mnepv-150-volts-80-amps-array-breaker.html. Only be used up to 2000 watt array on a 24v battery bank when all is done in future
2. Midnite Kid up to 500 watts when all is done in the future.  Is this also http://www.solar-electric.com/midnite-solar-mnepv-30-amps-circuit-breaker.html

I know some of these question might be repeating myself but trying to make sure it is done right. 
1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter

Comments

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    If you can spare the space, go for the big baby box.  The breakers you mention are sized OK... just make sure the ampacity of your wiring exceeds the breaker size.  

    Those din rail breakers are polarized.... do you know which side goes to the controller and which side goes to the battery?

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Zakarume
    Zakarume Solar Expert Posts: 143 ✭✭
    Options
    Have not gotten the breakers yet. Just getting feedback right now to make sure i get the correct ones and i do it right. I checked to size difference between both boxes and really not that much different, just a few inches. So i will go with the Big Baby box. If you can link the breakers and box
    1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options

    Hi Zak..,

    vtmaps is correct,  the MN Baby Box,  is tiny.

    The Big Baby is considerably larger.   So this box will handle ONLY  the CC output breakers  ...  meaning that the Input breakers for the CCs are in a different box?   As you know,  each of these two CCs will require an input breaker,  as well as an output breaker.

    Also,  as you know,  the Big Baby will accept four DIN Rail breaker spaces,  that 80 A double-wide breaker occupies two spaces,  and the MNEPV 30A breaker occupies only one space,  but there would not be enough space to also have two MNEPV input breakers in the BB box,  as well.

    FWIW,  Vic

    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Zakarume
    Zakarume Solar Expert Posts: 143 ✭✭
    Options
    I am going to get the Big Baby Box along with busbars. Just now making sure i get the right breakers. If anyone can link the 2 breakers please do so. In case you are still wondering. Will get a Midnite classic 150 and Midnite kid. Wire size 6 gauge
    1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    edited February 2016 #6
    Options
    Zakarume said:
    I am going to get the Big Baby Box along with busbars. Just now making sure i get the right breakers. If anyone can link the 2 breakers please do so. In case you are still wondering. Will get a Midnite classic 150 and Midnite kid. Wire size 6 gauge


     1.  OK,  but,  first,  it is you who has Linked to those two breakers on the Wind-Sun site ...   what additional information do you need?

      2.  Did ask you about just where the additional breakers that are needed by the Charge Controllers  --  the Input breakers for each CC?  These can be MNEPV breakers,  BUT,  if they are not in another box,  you will not have room  for two input breakers,  the 80 Amp breaker,  which requires TWO DIN spaces,  plus the other output breaker  the MNEPV   30 A ...  this is five spaces  where four are provided.   SO,  is there another box that holds the two,  necessary additional breakers  --  the input breaker for each CC.

    Here is the info for the BB box on the MN site:
    http://www.midnitesolar.com/productPhoto.php?product_ID=122&productCatName=Small Breaker Boxes&productCat_ID=10&sortOrder=2&act=p

    Just trying to be clear,    Vic


    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Zakarume
    Zakarume Solar Expert Posts: 143 ✭✭
    edited February 2016 #7
    Options
    Sorry. This is what i have decided overall.
    1. http://www.midnitesolar.com/productPhoto.php?product_ID=122&productCatName=Small  This Box only with Busbars
    2. http://www.solar-electric.com/midnite-solar-mnepv-150-volts-80-amps-array-breaker.html.  For my array using Midnite classic 150 up to 2000 watts
    3. http://www.solar-electric.com/midnite-solar-mnepv-30-amps-circuit-breaker.html. For the smaller 500 array using Midnite Kid

    I hope this explains it better. A total of only 1 box, 2 breakers (30 & 80 amp)



    1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
  • zoneblue
    zoneblue Solar Expert Posts: 1,220 ✭✭✭✭
    Options

    you can also get the big baby in a versiion that takes the panel mount breakers. They come in a one pole 80A, and are unpolarised.
    1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
    http://zoneblue.org/cms/page.php?view=off-grid-solar


  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    edited February 2016 #9
    Options

    Hi again Zak..,

    OK,  fine on your decision ...
    BUT,  have tried to ask the following question twice before ...

    WHAT ARE YOU DOING/GOING TO DO FOR THOSE TWO NECESSARY (ADDITIONAL) CIRCUIT BREAKERS ON THE INPUT OF EACH CC??  Are they in (or going to be in) another MN Box,  with MN breakers ?? ?    ?    What is the plan,  if one might ask?

    And,  YES,  one does think about the MNEDC-Quad box that will accept up to four small Panel Mount breakers.  The DC Quad is a bit deeper than is the BB Box,  and is steel,  if that matters,  IIRC:
    http://www.solar-electric.com/installation-parts-and-equipment/midnite/elenanddcdi/mnedc-quad.html

    Here are the PM MNEDC breakers:
    http://www.solar-electric.com/pamodccibr.html

    FWIW,    Vic

    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Zakarume
    Zakarume Solar Expert Posts: 143 ✭✭
    Options
    I dont know any other way to explain this. All i want to do is get the Big Baby Box. Install it. Run the wire from Midnite Classic to the 80 amp breaker and run the 2nd wire from midnite kid to amp breaker and then to batteries.. Thats it
    1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Zakarume said:
    I dont know any other way to explain this. All i want to do is get the Big Baby Box. Install it. Run the wire from Midnite Classic to the 80 amp breaker and run the 2nd wire from midnite kid to amp breaker and then to batteries.. Thats it


    Great!    And each CC will WANT an additional breaker or DC-rated Disconnect on its INPUT.  These breakers will accept the output of any Combiner Box that is required on their input terminals,  and the output of each of these additional breakers  (or possibly,  but not likely,  a Disconnect switch)   will be connected to the INPUT of each CC.

    These additional breakers that are mentioned,  above,  are really REQUIRED  --  they will be something that you will also WANT,   IMO.

    That is all,  sorry for all of the SHOUTing,    Just FWIW,   Thanks,    Vic

    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • Zakarume
    Zakarume Solar Expert Posts: 143 ✭✭
    Options
    Vic sent you a private message
    1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
  • Xizang
    Xizang Registered Users Posts: 50 ✭✭
    Options
    None of these boxes seem to be outdoor weatherproof.   Anyone have outdoor boxes?   In particular, heavy gauge non-metallic (plastic) breaker boxes that would be suitable for marine use?   Saltwater has a habit of quickly eating up most metals (except maybe stainless and titanium)
  • Photowhit
    Photowhit Solar Expert Posts: 6,003 ✭✭✭✭✭
    Options

    I can't recall the brand, but I've rebuilt a positive ground combiner 'plastic' box for my combiner box;

    There are people making combiner boxes from non conductive material. Try;

    http://shoals.com/

    http://www.imagineinstruments.com/solar_combiner_box.html

    I know you want inexpensive as well and I haven't seen a breaker box for inverter size breakers in a non-conductive material. This likely has to do with the smoke hazard if inside as Zoneblue(?) or maybe Dave(?) has said in a pervious thread.

    You might want to just build one your self, hunt down a Non-conductive box, even used (try craigslist and eBay)since you will likely need many wires passing through the case, hunt down the proper water proof wire restraints and drill out the box your self. I added 4 to the above box.

    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).