Off Grid Battery Sizing
TFTI
Registered Users Posts: 1 ✭
I'm planning to install solar panels/use a propane generator for a battery backed off-grid system. I've been searching online and have found conflicting information in regards to sizing my batteries. I'll require 6,000watts for 14hours from all the electronics I plan to run. I'd need at minimum a one day autonomy. Looking to use L16's or a fork lift batery for a 48v system. Any help would be much appreciated.
Can someone confirm that this battery sizing calculator is correct?
https://www.batterystuff.com/kb/tools/solar-calculator.html
Welcome to the forum TFTI.
First, just to clarify, is that 6,000 Watts * 14 hours per day = 84,000 WH per day = 84 kWH per day
Or is that 6,000 WH (6 kWH) per day, over 14 hours (day time or night time)?
If it is the first, then, at a minimum, you are looking at:- 84,000 WH per day * 1/0.85 AC inverter eff * 1/48 VDC * 1 day storage * 1/0.50 maximum discharge = 4,118 AH @ 48 VDC battery bank
If your needs are otherwise (pumping water, moving air, running a cell tower, etc.)--Then you probably should review your loads and take a serious stab at conservation. Many people can cut 1/2 (or even more) from their electrical needs if they work at conservation (new Energy Star Equipment, turn stuff off when not in use, insulation, etc.).
In general, running a very large off grid solar power system (84 kWH per day is very large--That can power a very large home with full AC in Texas or Florida). Probably would need a proffesional installer if this is your first time and you don't have a lot of electrical/construction experience.
If it is only 6 kWH per day, that is reasonable small system that works well for DIY folks.