Charge voltage discrepancy on a Midnite Classic 150

Options
Saipro
Saipro Solar Expert Posts: 74 ✭✭
God knows I've scoured the Midnite fora for information on this but come up with nothing. Anyway, here it goes:

I have two different houses with similar systems. Equipment is otherwise identical. Configuration is not (24v and 48V). The PV panels, batteries and charge controllers are the same. Inverters are both the same make and 3kW but one is 24V, the other 48V. Recently changed one of the charge controllers from an EP Solar iTracer IT6415ND 60A to Midnite Classic 150. Everything appears to work fine and I have to admit, I'm more than impressed with the Chinese controller. Given, I had some misgivings earlier but that's history now. I swapped the controllers round after a month, just for kicks.

Here's the confounder: I live smack in the tropics and it's an oven out here right now. Set absorb to 28.8V to keep my batteries from deteriortating rapidly in the heat (Trojan T105-RE 6V). The classic shows 28.8V at absorb and so does every other piece of equipment. I transplant the Midnite to the 48V system. Double the absorb to 57.6V. A walkover, presumably. How wrong! From that point on, everything I do to make it jump to 57.6V fails. It reaches a peak of 57.0V and NEVER exceeds it. Every equipment tells me that's the exact voltage I'm reaching and not a system quirk.

Funny thing, my inverter can push it all the way up to 57.6V but I start smelling sulfur fumes. Not good for 6 month old batteries. I go back to charging with solar only. I have fairly reasonable grid supply so I never have to charge using generator and cut back on use on days when there's no grid power and the sun isn't out. On a typical day, both systems are at float by midday to 3pm (depending on overnight discharge and presence/absence of grid supply the previous day).

The question: is this behaviour of my 48V system normal or have I gone horribly wrong somewhere (the 24V system works flawlessly). If I have gone wrong, what is the remedy?
Semi off-grid

255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

Comments

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    What is the Vmp, and how are your panels configured on the 48 volt array?
    btw, this post shows up as 3 separate posts.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • zoneblue
    zoneblue Solar Expert Posts: 1,220 ✭✭✭✭
    Options
    Also check the temp compensation settings. You dont usually get exactly the same setpoint voltage because the temperature is not often exactly 25*C.
    1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
    http://zoneblue.org/cms/page.php?view=off-grid-solar


  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    Options
    vtmaps said:
    What is the Vmp, and how are your panels configured on the 48 volt array?
    btw, this post shows up as 3 separate posts.

    --vtMaps

    Sorry for the triple post (I hope the moderator deletes the replicates). Poor internet connectivity when I was making the post. Funny thing is, I clicked just twice. First time I got no repsonse so after about 5 minutes, I tried again and it notified me of admin ratification being required before it goes live.

    VoC is 37V and VmP is 29.4V
    Array is in three strings of three. 9 panels of 240W to make 2,160W raw, attained on unusually clear and cool mornings. Seen 2,200+W on an occassion or two. Typically about 1,400W on the hottest of days to about 1,800+W on a typical day. Combined VoC varies with the day. Usually between 105 and 110V. VmP depends on SoC but with a discharged battery can drop to 69V but typically is within 72V and 80V. Everything else is as previously stated.

    Temperature compensation settings are standard. And are as stated on the panel nametag.
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    The multiple posts are a forum issue... Sometimes it decides that a post needs to be put into moderation. And the note that says posts goes into moderation only stays on screen for 1/2 second (and most of us miss that note)... So we type in the posts again (I did this too) and it goes in the moderation queue too.

    The Spam filter is working very well--But I need to figure out how to make it not put long term posters into the moderation queue. It can be done, but I don't have a lot of free time at the moment--Sorry.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    edited October 2015 #6
    Options
    Thanks Bill. By the way, do you ever sleep? You're always helpful and typical a heartbeat away on crucial issues.
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    You folks are pretty well behaved--Does not take too much time these days (long posts always take a bit of work).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Back to the charging issue... is this 57 volt ceiling affecting the batteries?  That is, have you checked the SG of the batteries?  If the batteries are warm enough then 57 volts might be high enough,

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    Options
    SG is as expected. Electrolyte bubbles just fine. Batteries warm a tad bit (about a degree centigrade or two) and performance seems uncompromised (I know by the time I see a performance degradation, it's already too late).

    The Trojan guide says 2.35 - 2.45V/cell for absorb. The 56.8V I see at absorb is still sufficient for getting my cells to 2.366 at absorb. Considering I'm in the hot tropics, I believe I'm still okay. Nonetheless, Why am I getting 56.8V when my settings are clearly at 57.6V. I went one step further on two occassions and did not discharge the batteries, letting them go into absorb as early as possible the next morning. It's flattens out the voltage at 56.8V still.

    By the way, when I initially set it to 56.8V (my original intention), I was getting 55.9V - 56.1V hence the need to bump it up in the first instance. Thoroughly baffling
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    If you are in the hot tropics, it is possible that the discrepancy you noticed at the lower voltage setting is just the effect of temperature compensation.
    Some CCs display the uncorrected voltage while delivering the corrected voltage. I think that yours is showing you what actual voltage it is delivering based on applying the temperature correction to the set point.
    SMA SB 3000, old BP panels.
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Saipro said:
    The Trojan guide says 2.35 - 2.45V/cell for absorb. The 56.8V I see at absorb is still sufficient for getting my cells to 2.366 at absorb. Considering I'm in the hot tropics, I believe I'm still okay. Nonetheless, Why am I getting 56.8V when my settings are clearly at 57.6V.
    Inetdog's answer is correct.  In any case don't worry about it... you might even try setting your absorb voltage and/or absorb time a bit lower.  Your goal should be to find the minimum absorb voltage and time that gets the SG up to 100% SOC.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    Options
    Just one last question. The houses are roughly kilometer apart. Why would the 48V system behave in this manner (temperature compensation) while the 24V system wouldn't (recombining the batteries in the 48V to form 24V double capacity has 28.8V showing as 28.8V)?
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Saipro said:
    Why would the 48V system behave in this manner (temperature compensation) while the 24V system wouldn't (recombining the batteries in the 48V to form 24V double capacity has 28.8V showing as 28.8V)?
    Are the batteries in the 24 volt system cooler than the batteries in the 48 volt system?  If they are just as warm, then It appears that the temp compensation is not working on the 24 volt system. 

    --vtMaps

    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    edited October 2015 #14
    Options
    Good answer. A quick check: I really don't wanna start another battery thread but I think one should exist as a compendium of sorts for the popular battery types and brands (limited to the ones specified for RE use, lest the thread grows out of hand). Strictly informative and not a Q&A thread. Mine is regarding the Trojan T105-RE batteries. Disregarding the variations in humidity and temperature (assuming STP), what would you recommend as

    (1) absorb charge duration (I use 3 hours and have a daily DoD between 20% and 40%)?
    (2) absorb voltage limits per cell (manual states 2.35V - 2.45V but I'm thinking bigger batteries with thicker plates like the L16-RE or the IND17 can't possibly share the same absorb voltages as the comparatively tiny T105-RE even though the manuals state the same voltage limits for them all)?
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Saipro said:
    what would you recommend as

    (1) absorb charge duration (I use 3 hours and have a daily DoD between 20% and 40%)?
    (2) absorb voltage limits per cell (manual states 2.35V - 2.45V but I'm thinking bigger batteries with thicker plates like the L16-RE or the IND17 can't possibly share the same absorb voltages as the comparatively tiny T105-RE even though the manuals state the same voltage limits for them all)?
    They certainly can share the same voltage, but the timing may be different.  The voltages that are used to charge a battery depend very much upon the charging protocol.  For example, industrial battery chargers may use the terms 'bulk' and 'absorb' differently than the typical RE equipment.  Even the popular Iota battery chargers specify bulk and absorb to have different voltages, something that makes no sense with a RE charger.  Read more here.

    You are fortunate to have flooded batteries.  That means you can check your SG.  Your goal should be to discover the minimum absorb voltage and absorb time that will get the batteries charged.  If your SG is good, then try lowering the absorb voltage by 0.1 or 0.2 volts.  See if the SG suffers.  If not, then lower it some more.  Find out what works for your batteries in your environment.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    Options
    Aargh! I've toiled sooo much to have my RE system in equilibrum as it were. To keep taking SG readings from my batteries? That's too much work, even to get paid for. Some greater enthusiast than I, somewhere must have collated a plethora of data relating to stuff like this else, am a keep staring those batteries in the eye till they go pop!
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • zoneblue
    zoneblue Solar Expert Posts: 1,220 ✭✭✭✭
    edited October 2015 #17
    Options
    What VT is talking about you only have to do to get a routine established.  But you should do definately do it. You only have two variables, absorb time and absorb voltage. If youre setup with WBJr you can get very precise on the absorb time. And Vts thinking on the voltage sounds sensible, if you remember that if you are tight on daylight hours a higher setpoint is sometimes needed to get the job done in the time available.

    The important thing is that the cells are actually gettting to 100% regularly. A little over for FLA is ok, a little under is not. (Hard sulphation and difficult to reverse capacity walkdown).To some extent a really decent float after the absorb will compensate for a prematurely terminated absorb. But again as VT said SG is the acid test. Pun is included free of charge.
    1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
    http://zoneblue.org/cms/page.php?view=off-grid-solar


  • Saipro
    Saipro Solar Expert Posts: 74 ✭✭
    Options
    .... acid test
    Pun ...... free of charge
    That's a double pun, if I ever saw one! I'll whip out my hydrometer and start taking serial SG measurements next week. I'll give feedback as appropriate (mind you, that's checking SG measurements twice daily for 24 cells).
    Semi off-grid

    255W Canadian Solar × 12, 200AH 48V US 185 XC2 bank, Victron Bluesolar MPPT 150/85, Victron CCGX, Victron MultiPlus 48V/5kVA/70A inverter (primary system) Victron Phoenix 48V/375VA inverter (backup for critical loads)

    300W Yingli × 2, Midnite Brat, 200AH 24V bank (powers DC LED security lights)

  • boB
    boB Solar Expert Posts: 1,030 ✭✭✭✭
    Options
    As far as voltage limiting, you might check the LIMITS menu to make sure that the highest battery temp compensation charge voltage is not set to 57.0 and limiting that.  It should be higher than this but just in case....  That feature is intended for sealed batteries but would work for flooded as well.  Love the puns !

    boB

  • PNjunction
    PNjunction Solar Expert Posts: 762 ✭✭✭
    Options
    SG's are great, but I know the slight voltage differences are driving you nuts too.

    Have you established a "standard" - that is if you are relying solely on the controllers display voltage, have you doublechecked that against your own voltmeter measured directly across the battery terminals?

    Slight discrepencies like 0.3, 0.6v differences or so can also mean that the measurement is being taken after a diode voltage drop.  Or, like mentioned above, the display value is slightly different from the real values.

    I'd vet out the accuracy of BOTH controllers with your own measurements at the terminals.  Even a low-end Fluke like a 11xx series should do fine, min-max hold and all that.  It doesn't have to be Fluke of course, and I don't want to turn this into a multimeter thread - but consider using something as a standard against which all others are compared to.