Xantrex 4024 Gen support amp problem!
90cummins
Solar Expert Posts: 57 ✭✭
I was trying to adjust the gen support amps from 14 to 30 amps today using my Xantrex System Control Panel and the maximum amperage it allows is 24 amps.
The range is 0-48 but if I keep increasing the value it returns to 0 after 24.
I have the manuals and cannot find anything that I've missed.
Your help would be greatly appreciated!!
Thanks 90cummins
Thanks 90cummins
Thanks 90cummins -
Maybe I am missing something (no expert here), but:
4,000 Watts / 240 VAC = 16.7 amps
And if I recall correctly, you can run a maximum current (from the inverter) on a single 120 VAC leg:
16.7 Amps * srt(2) = 24.6 amps maximum (~2,834 Watts max into a single 120 VAC load)
So, that might be the reason you are limited to 24 amps maximum.
The other possibility, what size do you have the AC2 Breaker input set to? It the value ~24 amps maximum? (or AC2 Breaker could be 24 amps * 1.25 NEC derate = 30 amp genset breaker)
My two guesses.
yep, all the settings are interdependent, and some are derated, giving you sometimes double derating ! Yow. That's why I like the combox, to see what's coming in and going out, and I can tweak with the SCP to get it just right.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
That's the problem; I was thinking amps @ 120v the input is at 240v.
looks like I'll set it at 15amps = 3.6kw.
This is a great community, help when you need it!!
90cummins