Reactive and Active Power grid tie

Options
quique
quique Solar Expert Posts: 259 ✭✭
Hi

How does reactive power affect anything when connecting a GridTied inverter/central to the grid?

Comments

  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive and Active Power grid tie
    quique wrote: »
    Hi

    How does reactive power affect anything when connecting a GridTied inverter/central to the grid?
    1. The GTI will not in general produce any reactive power output. Its current output is by design exactly in phase with the applied voltage from the grid.
    2. A generator or standalone inverter on the other hand will produce a (sinusoidal) voltage output and will try to deliver whatever current is necessary to maintain that intended voltage output.

    Therefore if you have loads with a non-zero power factor, you cannot drive them solely from a GTI. You need to have another source (like the grid) connected to handle the reactive portion of the load.
    So, if you have just enough GTI output to handle the real power of your load, the reactive portion of the current will come and go through your POCO meter, not totaling up any net power consumption.

    There will be I2R losses in the wires corresponding to the reactive current, just as there would be without the GTI in the picture.

    When you are dealing with an off grid PV system or generator, you have the opposite problem. All of current must come from the same source and so the reactive current will cause heating in the output circuitry of the standalone inverter or the windings of the generator, limiting the output power actually available for the real part of the load to less than the full nominal output of the power source. For a well designed inverter, the current drawn from the battery will not be increased too much by the reactive power requirement of the load though.
    SMA SB 3000, old BP panels.
  • quique
    quique Solar Expert Posts: 259 ✭✭
    Options
    Reactive power vs Active Power

    How does reactive power affect anything when connecting a GridTied inverter/central to the grid?

    I just spent about an hour going through all the analogies for Active Power, Reactive Power and Apparent Power.

    Great so I understand its basically an efficiency issue. We actually pull more than we need because we need to offset that inefficiency caused by out-of-phase V & I.

    So Im looking at a table of power consumption of a company and it reads:

    KWARH = 105,258 (which would be Active Power, what you really need)
    KVARH = 43,436 (which would be Reactive Power, the offset)
    Demand = 565 (apparent Power, what you end up pulling)

    Analogies of marbles, beers and horse-pulled cars are great but tying them into whats actually happening is a bit more complex.

    Thanks
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: Reactive power vs Active Power

    I've merged these two threads because they are pretty much the same question.
  • quique
    quique Solar Expert Posts: 259 ✭✭
    Options
    Re: Reactive power vs Active Power

    Yes I did, I was looking for how to erase it from here but couldn't find it, sorry.

    And thanks for your answer but could I bother you for an "even simpler" explanation? If thats even possible :)

    Thanks
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power

    Thank you Coot.
    I got a little confusing as I was replying while you were merging. :)
    SMA SB 3000, old BP panels.
  • quique
    quique Solar Expert Posts: 259 ✭✭
    Options
    Re: Reactive power vs Active Power

    Thanks so much, I was looking for a way to erase the old one but could find it :)
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    quique wrote: »
    Yes I did, I was looking for how to erase it from here but couldn't find it, sorry.

    And thanks for your answer but could I bother you for an "even simpler" explanation? If thats even possible :)

    Thanks

    A GTI cannot, by design, supply any Reactive VoltAmps (VAR).
    So the VAR portion of the load must come from POCO.
    The GTI will supply what it can of the real power (Watts) and together the two will come up with the apparent power (VA) which goes into the load.

    I can try to clarify any particular subtopics of that if you like, but it may take awhile.
    SMA SB 3000, old BP panels.
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    Re: Reactive and Active Power grid tie
    inetdog wrote: »
    For a well designed inverter, the current drawn from the battery will not be increased too much by the reactive power requirement of the load though.

    As I understand it, some standalone inverters can put energy back into the battery or into capacitors. Or they can throw it away as heat. Or they can allow the voltage waveform to become distorted.

    I haven't seen any data on this effect although it it easy enough to measure.

    I am available for custom hardware/firmware development

  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    quique wrote: »
    Yes I did, I was looking for how to erase it from here but couldn't find it, sorry.
    AFAIK you cannot delete the thread once anyone has replied, but you can delete the original post using the Edit function.
    Go into Edit mode, find and hit the Delete button, then check the Delete radio button and hit the new Delete button that appeared when you first Deleted.
    Simple but not necessarily intuitive.
    SMA SB 3000, old BP panels.
  • quique
    quique Solar Expert Posts: 259 ✭✭
    Options
    Re: Reactive power vs Active Power

    Inetdog,

    So Im looking at a table of power consumption of a company and it reads:

    KWARH = 105,258 (which would be Active Power, what you really need)
    KVARH = 43,436 (which would be Reactive Power, the offset)
    Demand = 565 (apparent Power, what you end up pulling)

    Analogies of marbles, beers and horse-pulled cars are great but tying them into whats actually happening is a bit more complex.

    Can you shed light on these numbers :-)
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    quique wrote: »
    Inetdog,

    So Im looking at a table of power consumption of a company and it reads:

    KWARH = 105,258 (which would be Active Power, what you really need)
    KVARH = 43,436 (which would be Reactive Power, the offset)
    Demand = 565 (apparent Power, what you end up pulling)

    Analogies of marbles, beers and horse-pulled cars are great but tying them into whats actually happening is a bit more complex.

    Can you shed light on these numbers :-)
    Well, those numbers do not make any sense to me at all unless they are putting both apples and oranges into the same table.

    Based on my assumption that the first two numbers are energy consumed over some period of time (or a quantity with the same dimensional units where non-energy components like VAR come in) and the third number is a power consumption, for those users whose utility bill includes a per month charge based on the largest 15 minute consumption during that month. I would write it out as follows:

    Total real power consumption per month = 105,258 kWh (kilowatt-hours = units of energy.)
    Total Reactive power per month (which you do not get billed for at all) = 42,436 kVARh (same dimensional units as energy but does not represent any net energy at all)
    Total apparent power consumption per month (again, not what you get billed for) = 148,694 kVAh [which is exactly the sum of the first two] This line was not in their table!
    Peak power demand over the course of one month (which you may pay a per month fee for if a commercial user) = 565kW (not KVA, although some POCOs may charge for peak KVA rather than peak kW) Note that this is not directly related to any of the previous three numbers.

    If I had to guess, based on the bizarre mix of units etc, I would say the table came from the advertising brochure of a company selling Power Factor Correction snake oil. Or else from someone who did not understand the concepts involved. :)
    SMA SB 3000, old BP panels.
  • quique
    quique Solar Expert Posts: 259 ✭✭
    Options
    Re: Reactive power vs Active Power

    No, it's a table in excel, made by someone who works at the company in question.
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: Reactive power vs Active Power
    quique wrote: »
    No, it's a table in excel, made by someone who works at the company in question.

    That doesn't mean it has to make sense. :p

    Here's a clue for you: GTI's push current @ Voltage, even if the Voltage is not peak of the sine wave - just so long as it's in operating range. Loads with poor power factor pull current off peak of sine wave Voltage.
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    That doesn't mean it has to make sense. :p

    Here's a clue for you: GTI's push current @ Voltage, even if the Voltage is not peak of the sine wave - just so long as it's in operating range. Loads with poor power factor pull current off peak of sine wave Voltage.
    And here is something else for you to think about, Coot:
    GTIs push current at voltage but in such a way that the current is proportional to the voltage with the average over one cycle delivering the full available panel power averaged over that same cycle. Unless the reactive or non-linear load pulls so much current that it drops the voltage, the GTI will produce an output current with a power factor of 1.
    If the anomalous load is large enough to cause a voltage drop at some point in the cycle, the GTI may actually deliver less current at that part of the cycle.

    I am not sure whether that was what you were saying or not. :)
    "even if the Voltage is not peak of the sine wave" is a little murky to me at this time of night
    SMA SB 3000, old BP panels.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Reactive power vs Active Power

    I believe that SMA (or another European GT inverter mfg) has a GT inverter that can be programmed for +/- 0.80 PF -- I.e., they can "assist" with inductive (or capacitive) loads per the utility needs(?).

    The ability to produce non 1.0 PF is an interesting option. It does not change the power being generated (same solar array requirements). GT inverter has to have a bit more copper/iron to handle the higher output current (out of phase current).

    Will power companies require PF "uncorrected" GT inverters in the future?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • boB
    boB Solar Expert Posts: 1,030 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    BB. wrote: »
    I believe that SMA (or another European GT inverter mfg) has a GT inverter that can be programmed for +/- 0.80 PF -- I.e., they can "assist" with inductive (or capacitive) loads per the utility needs(?).

    The ability to produce non 1.0 PF is an interesting option. It does not change the power being generated (same solar array requirements). GT inverter has to have a bit more copper/iron to handle the higher output current (out of phase current).

    Will power companies require PF "uncorrected" GT inverters in the future?

    -Bill


    There has been talk of this but is done on large scale GTI's now, already I believe.

    The old Trace SW inverter was a voltage source GTI as well as the Outback GFX inverter...
    They only produce low current distortion when driving a low distortion voltage grid source.

    So, I think they will actually do this to a certain extent, unless something has changed in
    past years.

    It kind of makes sense that this should be an option because it can help to fix up the grid voltage
    when it is ugly. It's just a matter of feedback technique in the GTI and SMOP (Simple Matter
    Of Programming)

    boB
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power
    boB wrote: »
    There has been talk of this but is done on large scale GTI's now, already I believe.

    The old Trace SW inverter was a voltage source GTI as well as the Outback GFX inverter...
    They only produce low current distortion when driving a low distortion voltage grid source.

    So, I think they will actually do this to a certain extent, unless something has changed in
    past years.

    It kind of makes sense that this should be an option because it can help to fix up the grid voltage
    when it is ugly. It's just a matter of feedback technique in the GTI and SMOP (Simple Matter
    Of Programming)

    boB
    Well, it may be a simple matter of programming once the GTI has the needed input information. To be able to supply reactive power as needed, the GTI would have to be interfaced to a current transformer which reads the current to local loads. Not the output current of the GTI or the current to/from POCO.

    Kind of like not being able to control End Absorb current correctly unless you have a shunt on the battery.

    Otherwise the best the programming would do is to try its best to "correct" any observed distortion in the sine wave voltage applied to its terminals. And that in turn would have to assume that were is not for local loads the voltage from POCO would be distortion free. If the POCO voltage with no local loads is distorted, the GTI will waste output current trying to bail out POCO and will not get paid anything for the pure reactive power component.
    And even delivering the reactive component of the local load would increase the IR losses in the GTI output just to reduce a drain on POCO that you are not being charged for.

    Utility scale GTI installations might well get paid a bonus by POCO for helping with the reactive power demand. Or at least might reduce the low power factor penalty charge that some commercial users pay for local loads' consumption.
    SMA SB 3000, old BP panels.
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power

    > Will power companies require PF "uncorrected" GT inverters in the future?

    I believe that Germany is requiring GTIs to produce .95 lagging now. Ie, they don't want 1.0.

    I am available for custom hardware/firmware development

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Re: Reactive power vs Active Power

    A GT inverter (as I understand) can feed an arbitrary PF (or even current wave form) back to the grid--But this would be "open loop" (i.e., a software setting that simply tells the inverter what to output).

    If some sort of feedback was provided (such as a current tap transformer) could be used to "balance" local PF issues. Or the inverter could be connected to a receiver/Internet and be told by the utility what PF/waveform to supply.

    I believe Germany is looking at or even has some sort of utility active feedback requirement to throttle GT inverters (even for homes) now (days when lots of power and little power usage could overwhelm ability of "local grid" to manage excess power fed back into the grid.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    Re: Reactive power vs Active Power

    I agree that communications would make it a better system. I wonder how well the communications are protected from hackers. Looks like most of the systems impose a ripple signal on the power to communicate.