dump load

Options
dkpro1
dkpro1 Registered Users Posts: 16 ✭✭
I am looking to do this when my batteries reach 14.85 a motoring circuit would activate a relay and execces power would go to hot water heater element when it see 14.5 it would open circuit....any one know how to build this

Comments

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: dump load
    dkpro1 wrote: »
    I am looking to do this when my batteries reach 14.85 a motoring circuit would activate a relay and execces power would go to hot water heater element when it see 14.5 it would open circuit....any one know how to build this

    This is what we call an opportunity load: batteries charged and panels capable of more output than is being used to you take the opportunity to run something and make use of power that would otherwise be lost.

    There are several ways to do it, depending on what equipment you have now. Some of the higher-end charge controllers for example have programmable AUX ports which can be used to activate a specific load under certain conditions such as the charge stage being Absorb or Float. The top of the line here is MidNite's Classic with its "waste not" function.

    Another way to do it is with a Voltage controlled switch which monitors the battery Voltage and turns the load on solely dependent on Voltage. A third way is to use another charge controller as a diversion controller which monitors battery Voltage and (hopefully) follows charge stage to send power to the load via PWM.

    Voltage controlled switch: http://www.solar-electric.com/volconswit.html
    Voltage controlled relay: http://www.solar-electric.com/moredr.html
    PWM controller on diversion load (bootm of page 2): http://lib.store.yahoo.net/lib/wind-sun/TSdatasheet.pdf
  • dkpro1
    dkpro1 Registered Users Posts: 16 ✭✭
    Options
    Re: dump load

    thank you just what i was looking for little high price but oh well


    This is what we call an opportunity load: batteries charged and panels capable of more output than is being used to you take the opportunity to run something and make use of power that would otherwise be lost.

    There are several ways to do it, depending on what equipment you have now. Some of the higher-end charge controllers for example have programmable AUX ports which can be used to activate a specific load under certain conditions such as the charge stage being Absorb or Float. The top of the line here is MidNite's Classic with its "waste not" function.

    Another way to do it is with a Voltage controlled switch which monitors the battery Voltage and turns the load on solely dependent on Voltage. A third way is to use another charge controller as a diversion controller which monitors battery Voltage and (hopefully) follows charge stage to send power to the load via PWM.

    Voltage controlled switch: http://www.solar-electric.com/volconswit.html
    Voltage controlled relay: http://www.solar-electric.com/moredr.html
    PWM controller on diversion load (bootm of page 2): http://lib.store.yahoo.net/lib/wind-sun/TSdatasheet.pdf
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Re: dump load
    dkpro1 wrote: »
    thank you just what i was looking for little high price but oh well

    It may not cost as much as you think... it depends on what components you already have in your system. Perhaps you should put your system components in your signature line.

    If you use a voltage controlled relay to do the switching, you need to have some way to prevent relay chatter. When the relay switches the load on, the battery voltage drops and the load is turned off, and then the battery voltage rebounds and the load is switched on, and then off and then on and then off...

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • dkpro1
    dkpro1 Registered Users Posts: 16 ✭✭
    Options
    Re: dump load
    vtmaps wrote: »
    It may not cost as much as you think... it depends on what components you already have in your system. Perhaps you should put your system components in your signature line.

    If you use a voltage controlled relay to do the switching, you need to have some way to prevent relay chatter. When the relay switches the load on, the battery voltage drops and the load is turned off, and then the battery voltage rebounds and the load is switched on, and then off and then on and then off...

    --vtMaps

    relay chatter.?


    try star 43 mppt 1.4 kw aray
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: dump load
    dkpro1 wrote: »
    relay chatter.?

    Depending on what the load is in comparison to the battery bank the addition of the load can pull the Voltage down below the point when the relay turned it on cause it to shut off which lets the Voltage come up again to where the relay clicks on, reengages the load, Voltage drops ... repeats rapidly.

    try star 43 mppt 1.4 kw aray

    If you could add the system Voltage and battery Amp hour capacity we'd have a better idea what you've got to work with.
  • dkpro1
    dkpro1 Registered Users Posts: 16 ✭✭
    Options
    Re: dump load
    Depending on what the load is in comparison to the battery bank the addition of the load can pull the Voltage down below the point when the relay turned it on cause it to shut off which lets the Voltage come up again to where the relay clicks on, reengages the load, Voltage drops ... repeats rapidly.






    If you could add the system Voltage and battery Amp hour capacity we'd have a better idea what you've got to work with.



    540 amph bank @ 12 volt running 24 volt .......the load willl be 400 watts when sen. sees 29.6 load will stay on till sen. sees 28.4 this will keep me in absorb
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: dump load
    dkpro1 wrote: »
    540 amph bank @ 12 volt running 24 volt .......the load willl be 400 watts when sen. sees 29.6 load will stay on till sen. sees 28.4 this will keep me in absorb

    Absorb starts out at high current and tapers off. At the end the Amps should be down around 2%, or in this case about 10 Amps. That's 240 Watts from the 1.4kW (about 1kW derated) array leaves 800 or so available for your 400 Watt load (not including other loads). But again that's at the end of Absorb. What's the current like at the beginning? About 45 maximum yes but when you enter Absorb stage what kind of current do you usually see?

    400 Watts on 24 Volts (28 actually) will be around 14 Amps. If the current to the batteries and other loads is <30 it should handle it.
  • dkpro1
    dkpro1 Registered Users Posts: 16 ✭✭
    Options
    Re: dump load
    Absorb starts out at high current and tapers off. At the end the Amps should be down around 2%, or in this case about 10 Amps. That's 240 Watts from the 1.4kW (about 1kW derated) array leaves 800 or so available for your 400 Watt load (not including other loads). But again that's at the end of Absorb. What's the current like at the beginning? About 45 maximum yes but when you enter Absorb stage what kind of current do you usually see?

    400 Watts on 24 Volts (28 actually) will be around 14 Amps. If the current to the batteries and other loads is <30 it should handle it.

    43 -45 amps but have 15 amp load frig. and freez. running
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: dump load
    dkpro1 wrote: »
    43 -45 amps but have 15 amp load frig. and freez. running

    If the current draw is that high when the opportunity load kicks on you will definitely have trouble: there's no doubt that the added load will cause Voltage sag and the resulting relay chatter.

    This is one of those instances where you want to rethink the design. I'm not sure you have any surplus power available to use under the circumstances.
  • dkpro1
    dkpro1 Registered Users Posts: 16 ✭✭
    Options
    Re: dump load
    If the current draw is that high when the opportunity load kicks on you will definitely have trouble: there's no doubt that the added load will cause Voltage sag and the resulting relay chatter.

    This is one of those instances where you want to rethink the design. I'm not sure you have any surplus power available to use under the circumstances.

    im producing 1110 watts when i hit absorb... my load then is 200 watts when relay sees 14.9 will dump power to water heater leaving 500 to bank ...when it see 14.2 it will stop relay will open and close a little for first hour till bank is almost full then most of the power will go to heater