XW6048-Low Battery Cut Out vs Grid Support Voltage

Options
fca1
fca1 Solar Expert Posts: 124 ✭✭
Doing some testing i get the the gridsupport voltage must be 4v higher than the LBCO...
is there away to change this ...
i want to have the LBCO at 48 and the grid support at 49....
and now to have the grid support at 49 i have to setup the LBCO at 45 :(

Regards

Comments

  • NorthGuy
    NorthGuy Solar Expert Posts: 1,913 ✭✭
    Options
    Re: XW6048-Low Battery Cut Out vs Grid Support Voltage

    LBCO is when the inverter turns itself off. This shouldn't happen during normal operation, only when something extraordinary happens. It's a good idea to set it to 44V (typical) or below.